Hello,

My customer is in the process of turning an old outbuilding into a self contained flat. His spec includes 9kw shower, 3 x 3kw convector heaters, Oven with Hobs, 2 x -3-5kw under sink instantaneous water heaters, lighting and sockets.

It has been suggested that this is to be supplyed via the house 20-30m away which has an 80A 1361 service cutout.

After calculating the max demand and diversity for the proposed outbuilding installation i can't see how the 80A house service cutout will be able to supply this outbuilding as well as the original house?

Would it be recommended for the new self contained flat to be supplyed by it's own seperate dedicated DNO 80A supply?

Does anybody have any idea on the costs involved to do this?

or is it normal to run such a load off one supply? Whats the rule on domestic loads?

Any help much appreciated.

Thanks
 
Well, it's no good for your profit, but in my experience it is ultimately much cheaper to get the DNO to put a new supply in.

I've seen 3 wagons, six blokes and 2-3 hrs on site to do an install, for less than I could have bought the SWA for!!

Better technically too - loadings, metering, earthing.....
 
The total demand of the flat is likely to be approaching that of the house itself. Therefore the only sensible approach is to have a dedicated supply installed by the DNO.
 

Reply to the thread, titled "Domstic overload" which is posted in Australia on Electricians Forums.

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

Daily, weekly or monthly email

Back
Top