So according to eufy I need a transformer with a 30va minimum rating. The BG transformer I used is only 8VA. The charge symbol comes on then dissapears, basically it’s charging half the time causing the doorbell battery to slowly drain.

They recommended this transformer off Amazon. 1 is £20ish and the other is £47.
The symbol below the square inside a square are different. I’ve tried to look up what the difference is and cannot find anything. The only thing is from the titles… one is continuous operation and other is discontinued service… what does that mean???
 

Attachments

  • IMG_3728.png
    IMG_3728.png
    996.2 KB · Views: 36
  • IMG_3727.png
    IMG_3727.png
    801.7 KB · Views: 29
They are both 30VA but only the continuous rated one can operate with a constant load of 1.25A. Apply a constant load of 1.25A to the other one it will overheat as it is designed for short instances of use such as a doorbell.
Most 230/110v site transformers are not continuous at their peak rating for example, a 5KVA one probably has a continuous rating of 3KVA with the 5KVA being intermittent.
 
They are both 30VA but only the continuous rated one can operate with a constant load of 1.25A. Apply a constant load of 1.25A to the other one it will overheat as it is designed for short instances of use such as a doorbell.
Most 230/110v site transformers are not continuous at their peak rating for example, a 5KVA one probably has a continuous rating of 3KVA with the 5KVA being intermittent.
When you say short instances of use such as a doorbell do you mean the old traditional ones and not the new type video doorbells?

From looking at the symbol, the continuous symbol appears to be on other bell transformers such as fusebox BG etc. but then looking at the discontinued service one it doesn’t have the bell symbol that looks like a pendant with a lampshade…

Annoyingly I can’t see which one of the two they recommended me because they sent it on the live chat thing and I ended up exiting to chat to them and it’s a nightmare to get through to them again
 

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

ppelec100

Arms
-
Joined
Location
London
If you're a qualified, trainee, or retired electrician - Which country is it that your work will be / is / was aimed at?
United Kingdom
What type of forum member are you?
Trainee Electrician

Thread Information

Title
Doorbell transformer symbols help
Prefix
N/A
Forum
UK Electrical Forum
Start date
Last reply date
Replies
3

Advert

Thread statistics

Created
ppelec100,
Last reply from
westward10,
Replies
3
Views
137

Advert

TrueNAS JBOD Storage Server

Back
Top