Hi guys can anyone help, few of the sparks over here in jersey are using 25mm double insulated flexible (15-16 strands) at supply intake for meters, 100Amp services single phase. My question is do you think the current carrying capacity will be higher on this type of cable than solid stranded standard (7 cores) reason I ask as it will allow me and the boys to not have to work with 35mm cables in trunking for 3 phase. 25mm only takes 89Amps 3phase in trunking. Clipped direct 114Amps. But if anyone has any info on this new D.I flexy it would be much appreciated. As there is a separate tri-rated table (it’s not tri-rated) I’m thinking maybe there could be one available for this new type cable! Much appreciated in advance ⚡
 
Double check with the manufacturers but IIRC it's the same CCC as 7 core.
Data sheet attached from Doncaster Cables.

Refers you to Table 4D1 of BS7671 for CCC.
Cheers lads yes just spoke to Doncaster cables to confirm, such a shame, they don’t do it in 35mm flexy yet but other manufacturers do.
 

Reply to Double insulated flexible 25mm (max amps.) in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
706
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
1K
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
3K

Similar threads

  • Question
This contactor you suggested unfortunately only has two NO switches rather than 1 NC and 1 NO required for the CR3 current sensing bypass...
Replies
14
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top