Gringoking88

-
DIY
Joined
Jun 18, 2015
Messages
176
Reaction score
58
Location
London
Hi all,

Tomorrow I am installing a cooker circuit and the client wants me to install 6mm on a 32amp breaker as she wants the flexibility moving forward to upgrade her cooker to a more powerful one.

At present her new cooker's instructions say it must be hard wired and protected using a 13amp fuse. Im looking for advice please on how best to add the fuse protection, e.g. would you take a feed from the connection unit to a FCU and then to the oven or would you feed a 6mm to a 13amp FCU and wire straight to this baring in mind its on a 32amp breaker?

I know its a basic question and apologise in advance so please be gentle. I am registered with NICEIC but hardly do any work tbh so am not involved full time and only tend to do small jobs for friends etc and want to make sure im doing this as safely and best as possible.

Many thanks,

M
 
^ Above - was the existing oven on a 13 amp plug socket then? i had assumed it was on a ccu and you wanted to change it to a fcu? but why have a fcu where it cant be reached? it sort of defeats having a switch if you cant use it

Gavin,

Believe it or not, the oven was wired straight into the terminal block shown in the photo. I was thinking the following setup; MCB on board - 45amp cooker switch - fcu with flex outlet to cooker (based on all the helpful info above). Mainly because it would make it simple to upgrade.
 

Reply to downgrading a cooker circuit in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
315
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
841
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
954

Similar threads

  • Question
When you say plus kettle, does this indicate you are needing 13A socket/s on the island and a hob supply? and then an oven supply on a tall...
Replies
5
Views
689
I would put this down to 433.3.1(ii) - no overload protection needed because the load at the single socket can't overload the cable, being fused...
Replies
14
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top