Hi Guys

I know showers have been extensively covered on here, but this this is a slightly different question.

went to a job to replace 45amp shower switch, I noticed cable was damaged by heat, first thought maybe loose connection, so I started investigating, I noticed a 9.5kw shower on 6.00mm T&E cable enclosed in wall on 40 RCBO, I know without even looking that if it was clipped this might be ok but buried in wall no.

I explained situation to superviser and he was going to ask me to downgrade MCB. I was about to have a debate with him when I found further evidence of severe charring and at that point I said it needs rewiring, IR test showing L/E 0.14 M ohms.

My question is iz>=IN>=IB
downgrading MCB may cover IZ>IN but IB is not covered and my understanding is an MCB will aloow an overload of upto 1.45 times its rating in this case the current carrying capacity of the cable would be 34amps and the fixed load will pull more than this 46.4 for quite some time,thus damaging the cable, am I wrong? if I am in this situation again do I correct him?

thanks in advance for your help
 
L-E of 0.14 Meg ohms would surely trip the rcbo if the cable was as faulty as that. Was it tested with neons disconnected etc
Ohms law suggests it wouldn't with only around one-and-a-half milliamps flowing.

In answer to the OP's question though, a circuit breaker should not be used as a load-limiting device,
 
It's interesting the number of sparks that are defensive of 9.5kw on 6.0mm. If it is designed and calculated right that's fine. Me personally I err on the side of caution, I've been to a few house fires on emergency call out.
That's probably because they've been asked to replace the existing shower, because it spits a tiny bit of hot water in the winter months with something more powerful, and just connected to an existing 32amp supply and replace the mcb with a 40amp.
 
I can't tell you the complete laws of thermal dynamics or heat transference. It is like that at the switch and 30cm up from the switch. I ve seen quite a few instances of heat damaged cables the fishy smell is present
 
I can't tell you the complete laws of thermal dynamics or heat transference. It is like that at the switch and 30cm up from the switch. I ve seen quite a few instances of heat damaged cables the fishy smell is present

I've worked in one or two houses that had a fishy smell too. Had no cables burning though :D

Ohms law suggests it wouldn't with only around one-and-a-half milliamps flowing.

In answer to the OP's question though, a circuit breaker should not be used as a load-limiting device,

Yeah didn't have time to work it out this morning. You're right of course :)
 
if Ib > Iz ( dependent on reference method of installation) then the cable is inadequate, irrespective of OCPD rating. end of.
 
Best EV Chargers by Electrical2Go! The official electric vehicle charger supplier.

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Green 2 Go Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses Heating 2 Go
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

Joined

Thread Information

Title
Downgrading MCB to protect cable but has fixed load greater than IZ
Prefix
N/A
Forum
UK Electrical Forum
Start date
Last reply date
Replies
22
Unsolved
--

Advert

Thread statistics

Created
gooner80,
Last reply from
telectrix,
Replies
22
Views
6,190

Advert

Back
Top