Hi all

I doing an eicr in a hotel. In the bathroom they have downlighters, some with 12v transformers some with LED GU10 fittings.

In a large majority of cases, there are plastic connectors on both sides of the transformers, no junction box, in free air laying on the ceiling.

Would you Code 1 the low voltage side & Code 2 the extra low voltage side or Code 2 both sides.

Your thoughts and advice will be gratefully received.
 
Code 2. They are not immediately accessible as such, but they are a potential danger yes.

You may be even able to argue Code 3, depending on the actual terminations. If just a choc block then Code 2 in my view.
 
Code 2. They are not immediately accessible as such, but they are a potential danger yes.

You may be even able to argue Code 3, depending on the actual terminations. If just a choc block then Code 2 in my view.

Many thanks Mr G Owl

I figured as much but wanted to be absolutely sure as there is an epidemic of these types of finish in this hotel.
 

Reply to Downlighter Connections in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
450
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
1K
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

  • Poll
Hi Folks, I'm looking for downlights that satisfy the following criteria: (1) white bezel; (2) fire-rated; (3) IP65 or above; (4) anti-glare...
Replies
0
Views
562
SOLVED Thanks for all the help. It was nothing to do with the smoke detector. In this new hole (where there will be a light fitting) three white...
    • Like
2
Replies
24
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top