MegOmz

Hi All
Might be an easy answer for most but I am just getting back in the game after 20 years...

I am time served and did my 18th last year, I have a question concerning selectivity. Here is the scenario. A domestic property has an 18th edition dual RCD board and one of the final circuits is providing a sub main to DB2 which is for an extension ( 40A 30898 MCB and 10mm T&E)
This DB is only 5 metres away in The utility room and is serving the new extension. DB2 is also RCD protected. If a fault occurs on a final circuit On DB2 It’s pot luck as to which RCD trips, DB1 or DB2.
what is the preferred (and BS7671 compliant) way if you were to swap out DB2? New CU with just MCB’s as it’s already protected by an upstream RCD? i don’t think you could move the mcb in DB1 to being unprotected as the sub main is buried and is T&E. I believe you would have the same issue even if you put RCBO’s in DB2, also if you were to perform an eicr what RCD trip times would you put on the sheet as three tests could trip DB1 and and two would be for DB2 so not really ideal
also don’t think you could use an S type in DB1 due to the disconnection times required.

thanks for reading !
 
You cannot use a time delayed device (30ma do not exist in the UK) as the 10.0 requires additional protection. One option is to ditch any rcd protection at DB2 this removes the rcd selectivity issue. If I were doing an EICR I would Code 3 it as it isn't really a safety issue, it is was it is.
As for recording/testing the rcds I would take the upstream device out of the question to test the downstream device but that is just me and not something I would necessarily demonstrate.
 
You cannot use a time delayed device (30ma do not exist in the UK) as the 10.0 requires additional protection. One option is to ditch any rcd protection at DB2 this removes the rcd selectivity issue. If I were doing an EICR I would Code 3 it as it isn't really a safety issue, it is was it is.
As for recording/testing the rcds I would take the upstream device out of the question to test the downstream device but that is just me and not something I would necessarily demonstrate.
Thanks for the quick reply - totally agree with the S type. my personal option would be to just have MCB’s in DB2 but just looking for clarification it’s OK. I can’t see why not and I have scoured BS7671 nothing specifically mentioned. as for the eicr I can see exactly where you are coming from, makes complete sense
thanks again
 
If it were not for the need to provide additional protection to the submain, there would be little difference between having the RCD protection in DB1 versus using an unprotected way in DB1 and a single RCD in DB2 as the main switch.

But if DB2 serves both lights and sockets in the extension, good practice would be to split those circuits across two RCDs or RCBOs so that one circuit can remain operational in the event of a fault on the other, just as you would split them across the two RCDs in DB1 if they originated there.

Clearly the need to protect the submain scuppers this, and possibly the lack of non-RCD ways in DB1 even if the submain were SWA. In this situation, stuck with an RCD in DB1, I would definitely avoid putting another in DB2.
 
If it were not for the need to provide additional protection to the submain, there would be little difference between having the RCD protection in DB1 versus using an unprotected way in DB1 and a single RCD in DB2 as the main switch.

But if DB2 serves both lights and sockets in the extension, good practice would be to split those circuits across two RCDs or RCBOs so that one circuit can remain operational in the event of a fault on the other, just as you would split them across the two RCDs in DB1 if they originated there.

Clearly the need to protect the submain scuppers this, and possibly the lack of non-RCD ways in DB1 even if the submain were SWA. In this situation, stuck with an RCD in DB1, I would definitely avoid putting another in DB2.
Thanks Lucien, much appreciated
 
This was my first post short of introducing myself. I have wanted to ask it for a while. I belong to a few electrical groups on Facebook and based on the responses I have seen for other questions I didn’t want to set myself up! This forum seems to be for people who actually want to help without ridicule.
having been out for a while It’s been interesting to see the changes. thanks again
 
I would either change the T+E to SWA so you can just use a non RCD protected mcb in DB1 or put DB2 as an rcbo in DB1 and swap the RCD with a main switch in DB2.

Just put a label on DB2 saying RCD protection provided at DB1, in the even of loss of power check at DB1.
 
He did say:
i don’t think you could move the mcb in DB1 to being unprotected as the sub main is buried and is T&E.
in which I took 'buried' to mean possibly at a depth requiring additional protection. But it is a good point that this was not confirmed as a fact.
 

Reply to Downstream RCD in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
373
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
938
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

  • Question
Thank you for taking the time to help explain this - much appreciated
Replies
7
Views
866
  • Question
ok cheers for the help lads
Replies
7
Views
708

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top