Hi All
Might be an easy answer for most but I am just getting back in the game after 20 years...

I am time served and did my 18th last year, I have a question concerning selectivity. Here is the scenario. A domestic property has an 18th edition dual RCD board and one of the final circuits is providing a sub main to DB2 which is for an extension ( 40A 30898 MCB and 10mm T&E)
This DB is only 5 metres away in The utility room and is serving the new extension. DB2 is also RCD protected. If a fault occurs on a final circuit On DB2 It’s pot luck as to which RCD trips, DB1 or DB2.
what is the preferred (and BS7671 compliant) way if you were to swap out DB2? New CU with just MCB’s as it’s already protected by an upstream RCD? i don’t think you could move the mcb in DB1 to being unprotected as the sub main is buried and is T&E. I believe you would have the same issue even if you put RCBO’s in DB2, also if you were to perform an eicr what RCD trip times would you put on the sheet as three tests could trip DB1 and and two would be for DB2 so not really ideal
also don’t think you could use an S type in DB1 due to the disconnection times required.

thanks for reading !
 
Could you say....

Isolator/RCBO40amp(Feed DB2)/RCD(circuits)/RCD(Circuits) if you have space in the board.

Have fun.
Hi Moose
if You put RCDs in DB2 would you have the same issue with tripping? it could trip the RCBO in DB1 or the RCDs in DB2.
also DB1 is already a split load board with two RCD,s. or have I miss understood? Sorry if I have
thanks
 
I was Just thinking if you placed DB2 in the utility room on its own circuit within DB1 moving the new RCBO 40amp to feed new DB2 next to the Isolator. Not apart of the RCD split board circuits.

Isolator - Feeds new RCBO. and x2 RCDs within DB1

I am assuming the protection of the Feeder cable to DB2 is by BD1. Will only trip Extension.
I am assuming yes it will trip off all circuits in Utility room. Unknown x Circuits?
I am assuming Fault Future, be solved by circuit elimination to get power up and running.
My assumption, Home owners do this with split boards Left side or Right side now. Then get a qualified man like yourself to fix the issue.

Others can quote regs for better fun to the story so far.

Have fun.
 
It’s pot luck as to which RCD trips, DB1 or DB2.
Or quite likely, both of them.
Unless they have significantly different tripping times, the slower device is likely already to be "in motion" on it's way to tripping by the time the faster one actually opens the circuit and removes the trigger current. I don't know what the time lag is between "irretrievably on it's way to opening" and "contacts opened" for a typical RCD, but I'd imagine it's a significant part of the tripping time.
 
If you have a DB fed off another DB using a MCB, RCBO, or RCD/MCB combination you will have poor selectivity.

The best you could hope for in this situation (vulnerable 10mm T&E) is to have the supply off, say a 45A C-curve RCBO and ditch the RCD in the sub-DB. But it is still going to be poor selectivity, due to several circuits sharing the same RCD trip, and that down-stream MCBs will probably also trip the RCBO on over-current fuse-blowing faults (PSSC above 225A might trip the feed RCBO).

Now that is not dangerous, just poor design and inconvenient.

If you really want to fix it, you would need SWA sub-main off a fused-switch and split the tails feeding the main DB. Then you might get away with a 50A fuse or so, and have a sporting chance of selectivity with down-stream MCB or RCBOs. But the cost & time of doing that might be too much.

In any case, for a new year, and hopefully for a better year!
 

Reply to Downstream RCD in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
373
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
938
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

  • Question
Thank you for taking the time to help explain this - much appreciated
Replies
7
Views
866
  • Question
ok cheers for the help lads
Replies
7
Views
708

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top