I am required to provide power to a shed, a pond (with pump) and some outside lights.
The lights are class 1 and are the drive over type.
The current earthing arrangement is PME.
This installation is in a garden with kids and animals present.

I have decided to install a CU in the shed and TT and spike it.
Reason being there will be plenty of Extreniuos conductive components from the pond and lighting.

I understand the need for the spike and the 16mm^2 bonding between the CU and the spike.
However looking at the osg its suggest a minimum 6mm bonding for water pipes ect.

The drive over lights, these are class 1 and will have extraneous condctive parts that are easily accesable by kids and dogs with wet feet ect. Will theese require the 6mm bonding as well?
They only have small 1mm terminals so i dont see how.
Tom be honest this is the first time i have installed lights that are easily touched...all of mine so far have been out of reach let alone actally in the floor.
 
Hi,

Hmm, I think you should revisit the definition for extraneous conductive parts before we go any further, and welcome to the forum.

Regards.
 
Hi Scuba,

Could you not extend the equipotential zone from the house by bringing the correct size 3 core SWA and using the 3rd core as the earth? Plus also bring a 10mm conductor for the bonding if required?

I'm not sure you would need the bonding cable if it is just the lights you are thinking about as I believe they would be classed as exposed conductive parts rather than extraneous and would be earthed by the supply cable that you bring to them.
 
Thanks for that..okay so i got my extraneous and exposed muddled up.
I had read the IET guidance note on electrical installations outdoors and hence why the mix of extreneous and exposed resulted in the decision to TT and spike.
With that cleared up i know understand i dont need to do that and can just extend the zone as mentioned earlier.
Thanks
 
just make sure that all class 1 equipment is earthed. record your R1+R2 and Zs readings on the cert.
 

Reply to Drive over ground lights bonding question? in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
349
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
896
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

The power company only brings in 3 wires which is 2 live and 1 neutral wire. It’s our responsibility to add the ground rod to bond the neutral...
Replies
3
Views
611
  • Question
Why would the RCD fail … yes it can happen but then it may not. Without it you have no protection on the TT System
Replies
36
Views
4K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top