Hi guys. Need to change the fuseboard at my parents house but none of their final circuits have a cpc run to them. Obviously have an earth on the main incoming so I can get a 16mm earthing conductor up to my new 18th edition metallic consumer unit but they don’t want a rewire so none of the final circuits will be protected with an earth.

My question is will this be an issue in the functionality of the rcds? Obviously the rcd functions on an imbalance between live and neutral so as far as I’m concerned it shouldn’t be too much of an issue hopefully, just wanted to get some of your opinions on the matter.

Another issue I can see is how I’m supposed to test for disconnection times without an
earth?

Opinions would be greatly appreciated

Thanks
 
are you sure of the no cpc? maybe on lighting, but all other circuits should have. what's the approx. age of the installation? are the circuits in metal conduit providing the cpc's? need more info. inc. pics.

and you can't possibly go ahead with a CU install without confirming presence of CPC's
 
Appreciate the speedy replies. I’ve not done any in depth research as yet, I just had a quick check of a 2 light switches while I was round there this evening having dinner. I will have to have a more in depth look now. Just thought I’d get some opinions on it before I did. I didn’t look for metal conduit in the back box but that makes perfect sense actually.
 
Appreciate the speedy replies. I’ve not done any in depth research as yet, I just had a quick check of a 2 light switches while I was round there this evening having dinner. I will have to have a more in depth look now. Just thought I’d get some opinions on it before I did. I didn’t look for metal conduit in the back box but that makes perfect sense actually.

Just because the lighting circuits (or maybe just the switch drops) don't incorporate a cpc you would assume all circuits don't have one??
 
One thing I did notice is there were 3 supply cables coming in but why would this be in a 3 bedroom house? A little over the top don’t you think?
get us some pictures. we love pictures. helps those of us that can't read grown-up writing. :p.
 
Appreciate the speedy replies. I’ve not done any in depth research as yet, I just had a quick check of a 2 light switches while I was round there this evening having dinner. I will have to have a more in depth look now. Just thought I’d get some opinions on it before I did. I didn’t look for metal conduit in the back box but that makes perfect sense actually.


If this is hoe you look into changing a cu, then my advice would be dont!!
 
It could be that the lighting circuits certainly don't have a cpc. It was not a requirement before 1966. This leaves you with the wiring being 53 years young and the problem of no cpcs in the lighting circuit. A rewire would/could be advisable.
 
If this is hoe you look into changing a cu, then my advice would be dont!!
Thanks for the advice big spark but I wasn’t looking into changing a fuseboard I was round my parents house for dinner and my dad threw it on me while I was there. I decided I’d have a VERY QUICK look while I was there and do some more digging when I have the time.
 
It could be that the lighting circuits certainly don't have a cpc. It was not a requirement before 1966. This leaves you with the wiring being 53 years young and the problem of no cpcs in the lighting circuit. A rewire would/could be advisable.

I’ve been telling them this for over 10 years to no avail. They don’t want the mess which is understandable. They are both in their 60s so I can’t see them ever having it done.
 
was normal for lighting circuits to not have cpc in 60's builds. if that's the case, it's OK to leave as is, but advise that only plastic fittings and switches should be used. if you take a light switch off, you'll probably see that the lugs for the faceplate screws are nylon, thus insulating the 3.5mm screws from the backbox.
 
I’ve been telling them this for over 10 years to no avail. They don’t want the mess which is understandable. They are both in their 60s so I can’t see them ever having it done.
if the wiring is in good condition, then there's no need for a rewire. maybe advise them to rewire the lightsalone, but as long as youensure insulated switches andlignts, no problem.

and the breers are taking toll.oopss maent beers.ach, gotit rigtht
 
was normal for lighting circuits to not have cpc in 60's builds. if that's the case, it's OK to leave as is, but advise that only plastic fittings and switches should be used. if you take a light switch off, you'll probably see that the lugs for the faceplate screws are nylon, thus insulating the 3.5mm screws from the backbox.
:D:D I told my father this before he went ahead and put all new metal switches on the whole of downstairs because they “look nicer”. Head + brick wall!
 
if the wiring is in good condition, then there's no need for a rewire. maybe advise them to rewire the lightsalone, but as long as youensure insulated switches andlignts, no problem.

and the breers are taking toll.oopss maent beers.ach, gotit rigtht
So In terms of the functionality of the rcds, you can’t see this being an issue? I would assume that if any exposed/extraneous conductive parts do become live and someone touches them and creates a fault path, that the rcd will pick up on this imbalance regardless?
 

Reply to Dual board with no earth on final circuits in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

  • Question
It is actually specified in BS7671 that the cpcs must be connected to all other sources of earth.
Replies
9
Views
667
  • Question
CONCLUSION (Couldn't see how to edit title) It was not belting it down with rain today, so lifted the manhole cover. The pump is about 2 metres...
2
Replies
45
Views
5K
  • Question
There could also be a completely unsuitable junction box embedded within the wall and tiled over or just cables in choc blocks in old accessory...
Replies
6
Views
823
In the 80's I was taught that with PME earthing arrangements we used 16mm for the main earthing conductor, some went a bit crazy and were bonding...
Replies
11
Views
1K
  • Question
BS3871 type 3's have a similar shaped operating curve to BS60898 type C's. Any fault that will meet the disconnection time of 5s (for 63A...
Replies
5
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock    No Thanks