Hi guys. Need to change the fuseboard at my parents house but none of their final circuits have a cpc run to them. Obviously have an earth on the main incoming so I can get a 16mm earthing conductor up to my new 18th edition metallic consumer unit but they don’t want a rewire so none of the final circuits will be protected with an earth.

My question is will this be an issue in the functionality of the rcds? Obviously the rcd functions on an imbalance between live and neutral so as far as I’m concerned it shouldn’t be too much of an issue hopefully, just wanted to get some of your opinions on the matter.

Another issue I can see is how I’m supposed to test for disconnection times without an
earth?

Opinions would be greatly appreciated

Thanks
 
just check the other circuits. bet you they all have cpc's. then if they insist on metal switches, check that their wills are in order.
 
So In terms of the functionality of the rcds, you can’t see this being an issue? I would assume that if any exposed/extraneous conductive parts do become live and someone touches them and creates a fault path, that the rcd will pick up on this imbalance regardless?

Yes if someone touches the parts and receives an electric shock the RCD will operate once the shock has become severe enough. And if that person is in good health they will find the experience painful but likely survive, if they are not in good health or they have a weak heart they may well not survive the experience.
 
Yes they are still like it :D stubborn as an old goat is my dad. What can I say
Be stubborn back then. Tell him no board swap unless cpc added or at the very least all metal accessories changed to plastic.
Show him the electrical safety first guide to help persuade that a real danger presently exists and that the correct course of action should be followed.
 
Lovely stuff! So as long as I make a note of it on the doc and the **** pile of other stuff I’m sure to find, my --- is covered?
you go to work on an ---? i thought even essex had horses these days.
 
just check the other circuits. bet you they all have cpc's. then if they insist on metal switches, check that their wills are in order.
:D:D:D If I end up changing the board I will remove all the metal switches and replace with Plastic while he’s not looking. Like I say though, for arguments sake, the rcd will still protect against this? Only problem being I can’t really test the theory out without an earth?
 
Lovely stuff! So as long as I make a note of it on the doc and the **** pile of other stuff I’m sure to find, my --- is covered?
A note on a cert cannot excuse you from the responsibility of not doing your job properly or leaving an unsafe condition.
 
, the rcd will still protect against this? Only problem being I can’t really test the theory out without an earth?

No, in this situation an RCD disconnects the circuit once a person is already receiving an electric shock. A 30mA RCD disconnects the supply before the shock reaches a level that is not normally fatal for a healthy adult.
 

Reply to Dual board with no earth on final circuits in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
382
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
963
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

  • Question
CONCLUSION (Couldn't see how to edit title) It was not belting it down with rain today, so lifted the manhole cover. The pump is about 2 metres...
2 3 4
Replies
45
Views
6K
  • Question
It is actually specified in BS7671 that the cpcs must be connected to all other sources of earth.
Replies
9
Views
774

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top