Dual earth terminals for computer circuits
B
brizospark
Noticed this on the architects notes can someone elaborate for me? thanks
the contractor should note the need for dual earth terminal blocks to be provided within DBs supplying computer power
IT equipment have high earth leakage currents so need 'High Integrity Earthing', the cpc should be connected to separate terminals on each socket on such a circuit and if it's a radial circuit a cpc should be taken from the last socket back to the DB.
Have a read of this...
http://electrical.------.org/wiring-matters/26/5437-earthing.cfm?type=pdf
I believe the type of earthing circuit depends on how high the total earth leakage current from the computers is.I am doing two rows of 4 and one of 2 at the moment,radials and each row has its own RCD.I will check the leakage current but I expect it to be very low.
if you ain't come across it before, you won't know. i know a few sparks who are " old school" had never heard of high integrity earthing till recently.
Well they should have because it is not "that" new, if they want to be classed as professionals then they must act as such.
Sorry my opinion stands, if the OP does not know then back off and get someone who does.
I thought the idea of this forum was to gain advice for things you are not sure about....the rudeness of some posters on here is breathtaking...........
I've just done a PIR on a large home office that had 10 PCs in and on day of test there was 27mA of earth leakage on the dedicated RCD circuit for those PCs (therefore approx 3mA per PC). Client reported occasional trips. Solution is another RCD as above. Thank heavens for the ramp test!
I did my apprenticeship in the sixties in maintenance and at the time "I knew it all"or so I thought
I found during my career,mainly installation, that others knew things I had no idea of
Conversely,they were blind to subjects I thought were fairly routine
You see where this is going to
The only thing I will say is this,
Electrical work is a vast area, and one that luckily is covered by someone or other on this forum
Reciprocating your knowledge is what the forum has been, and I hope will continue to be
Some give of their knowledge freely.others not so perhaps,but where would the forum be, without all of us lacking something or other to acquire
THATS THE SPIRIT DES!....Most posters on here are out to offer advice and guidance whilst gaining some themselves. I look at it like this...if it wasn`t for institutions like this forum you`d end up with loads of installs "going wrong" at some point or another: We need someware to share advice and have a laugh whilst doing so...we`d all go mad if we didn`t..lol..:grinningelf:
brizospark,
SW1970,