Dear all
Wonder if anyone can enlighten me
I've just changed a board to a dual rcd board. TT system with ze of 100 ohms
All circuits test ok and everything fine for 2 days . Had a call to say that while the customer was out ( so nothing in use) both rcds tripped at same time , they know this as two timer clocks ( one on each rcd side stopped at same time)
As far as I know it's only happened one , customer has asks what would cause it and I don't know so thought I would ask. I'm guessing it's something external but would appreciate anyone who can enlighten me
Cheers


Sent from my iPad using Tapatalk
 
Dear all
Wonder if anyone can enlighten me
I've just changed a board to a dual rcd board. TT system with ze of 100 ohms
All circuits test ok and everything fine for 2 days . Had a call to say that while the customer was out ( so nothing in use) both rcds tripped at same time , they know this as two timer clocks ( one on each rcd side stopped at same time)
As far as I know it's only happened one , customer has asks what would cause it and I don't know so thought I would ask. I'm guessing it's something external but would appreciate anyone who can enlighten me
Cheers


Sent from my iPad using Tapatalk
Dear all
Just thought I would update this one
Surprise suprise. Owner had done sone diy after I left and borrowed a neutral for his garage lighting so when turned on a light inside it tripped both rcds. Gota love em. Cheers for replies
 
Hi lee. I though s type were not intended for Personal shock protection as they are slower to react and could allow current to flow for an unacceptable period of time. Is this not the case ?
 
Ideally there should be an up front 100mA S type RCD to provide fault protection for the links between the main switch and RCD's.
Would only need up front s type, if the installation has a distribution circuit, simple tails and and bespoke gland would suffice, I believe.

Lee's correct again, when using A3 Dual RCD CU on TT :(. Apart from I thought the page number was 32-35 yellow OSG ;) (haven't got a yellow one yet myself), which advices using s type as main switch.
 

Reply to Dual rcd board tt system in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
279
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
775
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
783

Similar threads

  • Question
Generally speaking local earthing will rarely be below a couple of ohms, so in parallel with a TN-S sub-ohm value will make little difference...
Replies
4
Views
693
  • Question
What I find a little bit interesting is that there was an era of MFT's e.g. Robin, early Kewtech that tried to do non-trip loop tests using D-Lok...
Replies
5
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top