Called out today to fluorescent lights flashing on and off. Only 207v at fittings. after abit of a head scratch. Turns out they have had solar PV recently installed, a voltage optimiser was fitted at same time.
Found the optimiser, it had 3 outputs 10% 8% and 6% reductions, originally installed on 10%, so quick swap to 6% and voltage is at 216/217v just around the lower limit of allowed.
Any one come across these things before, and what's the point if it can't reliably keep the voltage within limits.
My thoughts are have it removed by original installers, for a refund