Good morning all, just after a wider view on this,

we have a large control panel which allows the company to test motors on. This allows the company to verify the condition of the motor after repairs. The motors are connected to the test panel by a series of sockets from 16a up to 500a outlets, the company then has test leads with the correctly selected cable for that outlet, the test cable has a plug on one end, and the other end is terminated into the motor terminals.

The test panel has a built-in Pilz safety relay which is supplied from a number of door/gate interlocks and e-stops around the test area. The safety relay controls a number of contactors within the control panel.

The question is, once the testing has been completed, the company hits the e-stop on the HMI control screen and places a safety lock through this e-stop. Then enters the test area, removes the plug from the socket and pre-dead at the motor terminals. (the e-stops a Idec XN4E-BL404MR)

To meet EAWR and the definition of “isolation,” would you say what the company has in place is adequate? If work is needed within the control panel itself, then the 400a isolator is turned off, secured and the panel pre-dead.

The plug and socket provide the disconnection and the E-stop via the safety relay provides the secure aspect?
 
Are you asking if the motor once unplugged is Isolated?
The E-stop offers the fail safe disconnect from supply, the plug the isolation, and from your question a LOTO procedure is in place. Not sure what your concerns are.
 
Last edited:
Changed thread title to e-stops a Idec XN4E-BL404MR. Please use longer titles for threads.
 
Changed thread title to e-stops a Idec XN4E-BL404MR. Please use longer titles for threads.
Which makes zero sense to anyone, not even a search engine. Maybe you should defer to your Admins/Mods who do understand these things a little more?
 

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

YOUR Unread Posts

Daily, weekly or monthly email

Thread starter

Joined
Location
gloucetser

Thread Information

Title
e-stops a Idec XN4E-BL404MR
Prefix
N/A
Forum
UK Electrical Forum
Start date
Last reply date
Replies
3

Thread Tags

Advert

Thread statistics

Created
dave992,
Last reply from
Rockingit,
Replies
3
Views
407

Advert

Back
Top