Ive been on 2 different jobs in the last few days that have stand by generators. one genny has to be manually started, and the other has an ATS.
There is one E stop inside the building on the main MCC, and multiple e-stops inside the generator container itself.
The problem is that the E-stops are required to be NO, and they are software inputs, and dont interrupt any contactor that shuts the engine down.
I think this is wrong, and they shoudl be fail safe. If the cable between the stops was cut, the system would still run, and without its e-stops.