[FONT=Arial, sans-serif]On a barn conversion for a client fitted 3 way garage c/u with rcbo's to supply 16 & 30 amp sockets for site supply. This is in a GRP box supplied by 3 phase supply from EDF. They required an earth rod to be put in to connect up to meter. Client now wants supply routed into basement. Questions: Will EDF be happy to extend the swa from[/FONT]
[FONT=Arial, sans-serif]transformer about 200 yards away into basement and put meter down there ? Would it be better to continue with external meter box and for me to run supply into basement and fit fused 3 phase isolator down there ?
Would you run 25mm tails in Conduit or use swa into basement about 15 m max
[/FONT]
[FONT=Arial, sans-serif]Another question: EDF have stated that 'PME will be provided 0.35 ohm so TN-C-S can be used if appropriate.' In 'area's of special risk' it is unlikely you can meet bonding requirements, so a TT system should be employed, and not to utilise the PME terminal. All circuits excluding Fire alarm will be on RCBO's. [/FONT]
[FONT=Arial, sans-serif]In what instance would I need to use an earth rod and not the PME ?[/FONT]
[FONT=Arial, sans-serif]As stated transformer is only 200 yards from supply.[/FONT]
[FONT=Arial, sans-serif]Thanks in advance.[/FONT]
[FONT=Arial, sans-serif]transformer about 200 yards away into basement and put meter down there ? Would it be better to continue with external meter box and for me to run supply into basement and fit fused 3 phase isolator down there ?
Would you run 25mm tails in Conduit or use swa into basement about 15 m max
[/FONT]
[FONT=Arial, sans-serif]Another question: EDF have stated that 'PME will be provided 0.35 ohm so TN-C-S can be used if appropriate.' In 'area's of special risk' it is unlikely you can meet bonding requirements, so a TT system should be employed, and not to utilise the PME terminal. All circuits excluding Fire alarm will be on RCBO's. [/FONT]
[FONT=Arial, sans-serif]In what instance would I need to use an earth rod and not the PME ?[/FONT]
[FONT=Arial, sans-serif]As stated transformer is only 200 yards from supply.[/FONT]
[FONT=Arial, sans-serif]Thanks in advance.[/FONT]