[FONT=Arial, sans-serif]On a barn conversion for a client fitted 3 way garage c/u with rcbo's to supply 16 & 30 amp sockets for site supply. This is in a GRP box supplied by 3 phase supply from EDF. They required an earth rod to be put in to connect up to meter. Client now wants supply routed into basement. Questions: Will EDF be happy to extend the swa from[/FONT]
[FONT=Arial, sans-serif]transformer about 200 yards away into basement and put meter down there ? Would it be better to continue with external meter box and for me to run supply into basement and fit fused 3 phase isolator down there ?

Would you run 25mm tails in Conduit or use swa into basement about 15 m max
[/FONT]

[FONT=Arial, sans-serif]Another question: EDF have stated that 'PME will be provided 0.35 ohm so TN-C-S can be used if appropriate.' In 'area's of special risk' it is unlikely you can meet bonding requirements, so a TT system should be employed, and not to utilise the PME terminal. All circuits excluding Fire alarm will be on RCBO's. [/FONT]
[FONT=Arial, sans-serif]In what instance would I need to use an earth rod and not the PME ?[/FONT]
[FONT=Arial, sans-serif]As stated transformer is only 200 yards from supply.[/FONT]


[FONT=Arial, sans-serif]Thanks in advance.[/FONT]
 
[FONT=Arial, sans-serif]On a barn conversion for a client fitted 3 way garage c/u with rcbo's to supply 16 & 30 amp sockets for site supply. This is in a GRP box supplied by 3 phase supply from EDF. They required an earth rod to be put in to connect up to meter. Client now wants supply routed into basement. Questions: Will EDF be happy to extend the swa from[/FONT]
[FONT=Arial, sans-serif]transformer about 200 yards away into basement and put meter down there ? Would it be better to continue with external meter box and for me to run supply into basement and fit fused 3 phase isolator down there ? [/FONT]

[FONT=Arial, sans-serif]Would you run 25mm tails in Conduit or use swa into basement about 15 m max[/FONT]


[FONT=Arial, sans-serif]Another question: EDF have stated that 'PME will be provided 0.35 ohm so TN-C-S can be used if appropriate.' In 'area's of special risk' it is unlikely you can meet bonding requirements, so a TT system should be employed, and not to utilise the PME terminal. All circuits excluding Fire alarm will be on RCBO's. [/FONT]
[FONT=Arial, sans-serif]In what instance would I need to use an earth rod and not the PME ?[/FONT]
[FONT=Arial, sans-serif]As stated transformer is only 200 yards from supply.[/FONT]


[FONT=Arial, sans-serif]Thanks in advance.[/FONT]

well, anywhere where it not fixed for a start

Look at the exclusions from using PME in BS7671:2008, all quoting the ESQCR's:

caravans
construction sites (except fixed building such as canteens)
marinas
mobile/transportable units

etc etc
 

Reply to Earth and Supply Two Questions in the Electrician Talk | All Countries area at ElectriciansForums.net

Similar Threads

Hence the former name for TNC-S, PME. Protective Multiple Earth.
Replies
5
Views
619
  • Question
Not a reliable indication of a fault! What RCD characteristics (and also why is an incomer needed here)? Have you done a global L+N IR test to...
Replies
6
Views
746
  • Question
Better/Smart/intelligent/expensive generators require two earth spikes set ~10-15m apart. They check the resistance between spikes and will...
Replies
5
Views
936
  • Question
I think there is a little truth in what the guy in the video says, but he makes more out of it than he should. A N-E fault on a circuit protected...
Replies
28
Views
1K
If the shared neutral is lost ,won`t you be getting 400v across both cottages? 2 phase US style but double the Voltage.
Replies
22
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock    No Thanks