Maxine

-
Joined
Aug 6, 2019
Messages
6
Reaction score
2
Location
Ws3 1ry
Hi, I am just after some advice. I am having new meters fitted and been told they need to be earth bonded? I've attached a photo as my friend thinks this has been done but I need to know before I book an electrician, so any help is appreciated, thank you

[ElectriciansForums.net] Earth bonding for meters


[ElectriciansForums.net] Earth bonding for meters
 
It has been done but it is in the wrong place.
It should be fitted on the cusomer side of the meter (which it is) but before and branch, which it isn't. So it needs to move up to the horizontal bit that comes out of the meter, before the T joint.
 
You have what appears to be a bonding cable at the bottom pipe.
The size needs to be confirmed as adequate,the bond needs to be made before any intersection,yours is in the wrong position,also the "do not remove" warning tag is all but destroyed
Employ a sparks to put it right
 
You have what appears to be a bonding cable at the bottom pipe.
The size needs to be confirmed as adequate,the bond needs to be made before any intersection,yours is in the wrong position,also the "do not remove" warning tag is all but destroyed
Employ a sparks to put it right
Thank you. Was hoping to keep expenses down but looks like it needs doing.
 
Hi, I am just after some advice. I am having new meters fitted and been told they need to be earth bonded? I've attached a photo as my friend thinks this has been done but I need to know before I book an electrician, so any help is appreciated, thank you

View attachment 51169

View attachment 51170
This is the Electricians, what is that copper tubing for. Remember I’m from the USA and want to learn y’alls way of doing
 
This is the Electricians, what is that copper tubing for. Remember I’m from the USA and want to learn y’alls way of doing
gas pies. and meter. sod it ... pipes, not pies. the bit with the yellow tape is incoming to meter. the copper behind is from meter to boiler/cooker/ etc.
 
Thank you. Was hoping to keep expenses down but looks like it needs doing.

I don't deal with domestic works, although I am qualified to do so.
however I do know 2 different competent domestic (part p) electricians that could sort this out for you.
they are both based in tamworth, so not far from you.
they are both time served, professional electricians who I call on for any works that fall out of my preferred line of work.

if you are not able to find someone willing to help on the forum, feel free to ask for there contact details.
 
I don't deal with domestic works, although I am qualified to do so.
however I do know 2 different competent domestic (part p) electricians that could sort this out for you.
they are both based in tamworth, so not far from you.
they are both time served, professional electricians who I call on for any works that fall out of my preferred line of work.

if you are not able to find someone willing to help on the forum, feel free to ask for there contact details.
Thank you. I have someone coming to give me a quote tomorrow, so I am happy for some comparison quotes. It's not just this, I need a safety switch for a cooker hood the shower isolation cord doesn't work, the extractor fan in the bathroom doesn't work and the ceiling light in the lounge is loose
Apart from that the house is great! Think I may need to marry an electrician, it would be cheaper in the long run...
 

Reply to Earth bonding for meters in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
380
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
956
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

Indeed it would be. But that would mean having 2 things to disconnect instead of one. More margin for error. Of course, any diligent spark would...
Replies
6
Views
668
loz2754
L
  • Question
If there's no main switch on the CU, then the RCD is doubling up as the main switch and everything is protected by it. If there is a main switch...
Replies
5
Views
772

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top