frank11

DIY
Joined
Sep 15, 2020
Messages
4
Reaction score
0
Location
West Midlands
Hi Electricans,
I am a homeowner with an earth bonding question I am receiving conflicting advice upon and hoping someone can help point me in the right direction.

A few years ago I had a full bathroom replacement via my insurance company and a bathroom installation company they supplied.
Earlier this year on a Thursday evening a bath was left on an overflowed for a few minutes or so.
On the following Sunday evening my wife got an electric shock when handling the taps in the sink, I worked out that if I turned the ground floor hallway light off the shocks stopped so I taped off the light switch so the light wasn't turned back on.
I called out a qualified electrician who was able to attend on the Thursday, by that time the offending water must have dried out as there was no longer any shocks coming from the tap but he carried out a number of tests which involved running cables from my fuseboard to the bathroom and concluded that the pipework running to the taps were missing an earth bond as plastic connectors had been used (which were added by the plumber who installed the bathroom a few years back) so from his testing he said beneath the plastic connectors his tests show a 'good' earth bond but above the plastic connectors there isn't an earth bond - I have included an image of the pipework beneath my sink so you can see the layout.
[ElectriciansForums.net] Earth Bonding In A Bathroom

The electrician said that to remedy the situation I would need an earth bond adding from beneath the plastic connector to above the plastic connector which is relatively easy for him to do.
The problem is he has stated the same problem applied to the bath taps which don't have an earth bond either so is assuming plastic connectors were also used on the piping to the bath taps.

There is a difficulty in the fact the bathroom fitter fitted a full tiled side to the bath instead of a bath panel so to access the pipework to the bath taps I need to rip off the tiles which form the bath panel and also then need to replace the side of the bath again.

I contacted the insurance company who have been in touch with the bathroom fitter who has disputed the electricians view that his plastic connectors are the cause of the problem and after I suggested to the insurance company that they appoint an independent electrician to provide a report (which I would pay for initially and to be refunded if their electrician said the lack of earth bonds are a problem) and they then said if I get quotes for the work they will get it sanctioned and cover the cost.

The electrician who initially pointed towards the need for earth bonds indicated a price of £140 for him to add earth bonds in but I had to find someone to quote to take off the 'bath panel' tiling and then replace it after the electrician has done his work. I have now contacted 2 separate bathroom fitters and on explaining the above background they don't agree that the earth bonds are needed so I am left wondering what to think.


Could any of you guide me as to whether these earth bonds are needed as although the taps do not give electric shocks now my worry is that an unseen leak occurs somewhere, connects the pipework to a live electrical connection somewhere and my 9 year old lad gets an electric shock.

So very long winded but thought it good to let you know all the info.
 
Plastic push fit connections are used widespread, We don’t link every bit of copper pipe nowadays.

the electrician that quoted to bond the pipes is having a go.

Unless he links every length of pipe every side of every fitting, which could, in the event of another fault, create live taps across the house!

upgrade your consumer unit, which would involve the EICR suggested, will pick up any nailed cables and would increase the safety of your installation.
 
I am not sure you could get a shock through two plastic connectors, and some damp wood. But anyway looking at your electrics, if you are concerned about safety etc. I suggest you upgrade your fusebox to a modern one with RCD protection as soon as possible. As an aside did you have a wet floor and bare feet when experiencing these shocks? I also wonder, when the bath actually leaked on Thursday, did no one else get a shock from the taps? Is it only you that got a shock some three days later? Were you touching both taps?

No wet floor (can't remember about bare feet)
No one got a shock until Sunday night but I worked out you only got a shock if the hallway light was on so maybe Friday and Saturday we happened to not use the taps when the light was on.
The shock happened if you only touched 1 tap
 
Hi Frank, for what it’s worth I agree with above posts - this incident was likely not caused by Mr Plumber using plastic fittings. After water leaks on the top floor it’s quite common for the downstairs lights to be affected.

The pic of your fuse box worries me as it seems to show a switch or junction box floating about?
 
Appreciate all your comments and guidance.

I'm not too concerned to find out where the offending section is where the issue was created when I had the leak as its now dried out (and I don't plan on having a leak) but more looking to find out whether having an earth bond would stop the taps getting live/producing an electric shock if there were a leak in the future.


It's ESSENTIAL that the source of the problem be found, whether it's a fault of the bathroom refit or pre-existing.
You can never know if you're going to have a leak and exactly the same conditions occour.

Having an RCD on the lighting circuit won't remove the issue, it's still possible to get a non lethal but uncomfortable shock without tripping an RCD.
Testing may not find the issue if it's a screw or nail only touching the Live.
Hopefully whoever you get in won't give up untill they've found the source of the problem.

If I was looking into it I'd use an Endoscope /Boroscope camera to look up into the floor through where the hall light is fixed, to avoid any unneccesary damage initially to see if there is anything obvious.
Next would be remove the bath panel and look under there.
 
skimmed through but agree with preceding posts. copper pipes under sink and bath, if preceded by plastic, are not extraneous and should not be bonded. the sparks who suggested this should be taken out and shot in the goolies, then sent on a course to understand the purpose of bonding. it seems you have an underlying fault which manifested iteself due to a water leak. sack both electrician and plumber, and then get an expert in each field to fix.
 
It is entirely possible that there is no fault with the electrics, a ceiling rose could be wired with no permanent live, even if it has a permanent live, the switched live is normally on the outside of the rose.

Any water creeping into the rose is likely to contact the switched live far before the permanent live. Tracking back through the wet woodwork in the house until it finds a path to earth.

If there is an rcd supplying the circuit, the path to earth through the timber and back to earth via multiple paths is going to trip the rcd well before any risk of shock occurs.

The simple fact is, the system installed because of its age is unable to detect the type of fault that occurred.

Modern rcd’s Or rcbo’s would have turned off the power, probably before the shock risk was there, but certainly the moment a shock was felt the power would be switched off as the device would trip in less than 0.03 seconds (less than a blink of an eye to the layman)
 
No wet floor (can't remember about bare feet)
No one got a shock until Sunday night but I worked out you only got a shock if the hallway light was on so maybe Friday and Saturday we happened to not use the taps when the light was on.
The shock happened if you only touched 1 tap
I had something not too dissimilar, a story I’ve recanted here many times. Long story, shortened. Complete bathroom refurb. Plumber was getting shocks when touching copper pipes and newly plastered wall. All walls in vicinity of bathroom had voltage to earth. Sometimes rcd would trip. Turns out previous owner had installed some dado rail on the landing years previously, with nail just nicking cable (stripper) to landing light.

As already said, get a competent electrician in to do some testing.
 
I'm reasonably confident if Emma Shaw was still alive she would be less than pleased to hear that comment.
Awful read that ?. Wonder if that was a factor in RCDs to all circuits Buried less than 50mm in the building fabric coming in not long after? Shows the importance of IR testing.
 
Awful read that ?. Wonder if that was a factor in RCDs to all circuits Buried less than 50mm in the building fabric coming in not long after? Shows the importance of IR testing.
but that wouldnot have identified the fault as the metal rack was fitted after the installation had been completed., and the fault was not there before.
 
That was a different case - the linked story involved cable damage at the time of construction, which had subsequently been certified as safe.
mybad. mixed up the 2. however, in the emma case, it seems that the fault was from cable to encosed metal stud that was not earthed/bonded. so a IR test would not pick it up.
 
My advice, as per other posts, get a proper electrician in to do an EICR and mention also the problem you experienced during the flood. Installing supplementary bonding will not solve the issue, (and as stated, may potentially make it more dangerous) the fault will still remain.
Speculating on what or not what it could be is no help to you. Over the years Most of us experienced sparks have come across similar faults before , (I know I have) and the faults have been identified as the same or similar to each of all the above mentioned so far, so yours could be anyone of them or something entirely different.

I would also recommend a consumer unit upgrade, modern consumer unit devices offer much better protection.
 

Reply to Earth Bonding In A Bathroom in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Hope everyone has had a great Christmas and here’s hoping we all have a better new year coming our way ! Remember our riches aren’t measured by...
    • Friendly
    • Like
Replies
11
Views
511
  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
754
  • Sticky
  • Article
Thanks so much for sharing this with us! I’ll definitely take a look, it seems like there are a lot of useful and interesting products. The idea...
    • Like
Replies
5
Views
2K

Similar threads

  • Question
The chances of any problem without the RCD are minimal, including it extremely negligible......with the supplementary, on a kin to Hannibal Lector...
Replies
6
Views
810
People who claim to be plumbers... and tilers... New bath fitted and the drain is accessible from the side and there are isolating valves on the...
    • Like
Replies
0
Views
254

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top