Earth Bonding on a Submain | Page 2 | on ElectriciansForums
Discuss Earth Bonding on a Submain in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net
The OP said he has a plastic pipe entering the garage. Not copper
So to test the plastic pipe you would disconnect your copper part and then test to MET, which would then give you a reading of ?? Remember it's plastic!
Er...yes,I meant a test should be on the copper section connected to the plastic section for those of a pendantic disposition. (if that makes sense).
Personally I'd do a visual 'test' to establish extraneousivity....(which doesnt make sense)
Mines a Guiness.
I'm assuming that all that is extending this TN-S equipotential zone, is the steel wire armour of the 4mm SWA cable?? Which if is the case, makes it all a bit of a mockery to main bond in 6mm or 10mmcopper!!
Not that the copper pipe will probably need bonding anyway!! lol!!
Thanks all, the upshot is..... (a) everyone likes drinking (b) I was a bit silly thinking that a bond was required there (c) the NIC man hadn't thought it through either.
and no I wouldn't have ever bonded a plastic pipe!!!
Cheers all!
An update, went back to site today for something else and the plumber has been at work. The sink as been replaced with a stainless one and its attached to the concrete wall. I repeated a test between the boards earth and the sink and got 700ohms - I'm presuming one of the screws has got the rebar.
So I could put a 6mm conductor between the board and the pipe (which is bigger than the supply conductors) - however this isn't a main protective bonding conductor as its not continuous
The other option is suppose it to stick in an earth rod and go TT but that's a right PITA.
Any thoughts?
Any thoughts?
Just that I'm glad you did as WP suggested, and tested it, rather than just thinking its fine because you can see a bit of plastic. Nice one.
One reason why you ALWAYS test and never assume that copper pipework after a plastic incomer isn't carrying an extraneous earth potential... Just hook up a pipe clamp to the copper pipe section, you can bet your last pound, it'll be providing better protection than a typical UK TT system will!! lol!!
Unless it was you that put the spikes in :)
Boydy
Reply to Earth Bonding on a Submain in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net
4-5 hours for 150? no chance, this is 2024, 150 for 2 hours maybe, that said an hour seems pretty quick, not sure he did the job right
Did this many times back in the 70s and 80s. You'd be faced with extending or modifying sometimes nearly new wiring in twin without earth, and...