I would say be careful when you're doing the IR test...

The wander lead doesn't play any part in a Class I IR test, so wouldn't need to be held against anything for the IR test to complete.

... but if the sides were metallic you'd be able to clip onto it.

There are many models of kettle, Class I, which have metallic bodies that are not earthed.
This is how they are designed, however, and shouldn't be failed out of hand.
A Class I kettle should always have an earthed element/heating plate, though.
 
Best way, without scraping hands etc. - Just clip earth lead onto long bladed screwdriver. Push hard onto base plate - @ 25A it might fizz a bit, but gets results.
 
The wander lead doesn't play any part in a Class I IR test, so wouldn't need to be held against anything for the IR test to complete.
No but if the body of the kettle were metal (which in this case it isn't otherwise there would be somewhere to clip the wander lead when doing the earth continuity) you'd get 500v on the body of the kettle, so care should be exercised.
 

Reply to Earth Continuity on Kettle in the Electrical Testing & PAT Testing Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
As the holiday season approaches, PCBWay is thrilled to announce their Christmas & New Year Promotions! Whether you’re an engineer or an...
Replies
0
Views
760
  • Article
Bloody Hell! Wishing you a speedy recovery and hope (if) anyone else involved is ok. Ivan
    • Friendly
    • Like
Replies
13
Views
1K
  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
976

Similar threads

  • Question
That would depend on the instrument. On my old BM10 when you press & hold the button it just powers up the inverter circuits to generate the...
Replies
5
Views
405
  • Question
Yes I touched on diverted neutrals when I went over guidance note 3 the first time but I’m doing a second round and going between all books whilst...
Replies
9
Views
631

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top