Any supplementary bonding in place? That would do it. (Parallel paths, as other have said.)
Follow along with the video below to see how to install our site as a web app on your home screen.
Note: This feature may not be available in some browsers.
Discuss Earth continuity in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net
Well think about it for a minute....do you have anything on the ring running through the bathroom i.e spur for heater, towel rail, fan without over run, shower pump..... all which may have sup bonding connected especially if an installation to previous 16th norm.
Or you could have the good ol' "useless cross bonding" under a boiler run back into a spur next to it. These would all cause unexpected low cpc end-end continuity results below the value of your L & N readings.
Yes really, if the readings were done at the board with all conductors disconnected at the time of testing which is perfectly possible then how would parallel paths come into it? if he tested around the ring with conductors still connected in the board then yes I agree very very likely parallel paths, there is more ways to kill a pig than just stabbing it.Really. 2 conductors of the same size having matching poor terminations to give identical readings...... so say both incorrect, based purely on the fact that cpc end to end is lower than expected value. Lottery odds that one. Obviously parallel earth paths.
Yes really, if the readings were done at the board with all conductors disconnected at the time of testing which is perfectly possible then how would parallel paths come into it? if he tested around the ring with conductors still connected in the board then yes I agree very very likely parallel paths, there is more ways to kill a pig than just stabbing it.
even so, it c an't provide a parallel path if the RFC conductors are all dissed from the CU.See my earlier post. If the heating is a gas boiler and fed from the RFC, and the gas supply is bonded, this may be the parallel path?
even so, it c an't provide a parallel path if the RFC conductors are all dissed from the CU.
Are you sure that the L-L & N-N are correct. A figure of 0.8ohms (2.5mm) suggest a cable length of over 100m? Whereas 0.6ohms (1.5mm) suggest a cable length of 50m. Just a thought.Hi there this is been happening in a few houses now I've been testing and im
a little confused, when testing my ring continuity my earth hasn't been the standard 1.67x bigger than live and neutral when using twin and earth 2.5 cable, what causes this? ...........today my neural and lives were 0.8ohms but my earth was only 0.6ohms which is well short ....
Errr.....cough, got mine out of a book. 100m of cable, is quite a large RFC? Can you assess you RFC length and then compare to your test results?Out of curiousity what is the formula for calculating length of run? Cheers