even so, it c an't provide a parallel path if the RFC conductors are all dissed from the CU.
A couple of water heaters spaced apart on the ring could easily provide a parallel path to the cpc and produce a lower r2 reading.
Follow along with the video below to see how to install our site as a web app on your home screen.
Note: This feature may not be available in some browsers.
Discuss Earth continuity in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net
even so, it c an't provide a parallel path if the RFC conductors are all dissed from the CU.
OP is saying he's testing at CU with ends disconnected, no appliances or loads connected.A couple of water heaters spaced apart on the ring could easily provide a parallel path to the cpc and produce a lower r2 reading.
OP is saying he's testing at CU with ends disconnected, no appliances or loads connected.
Dunno, think the OP is saying no such heaters present?But HandySparks is saying that if he had two water heaters spaced apart then there would be two cpc connections along with copper pipework connecting between, so these would reduce the resistance of the cpc (by effectively making a parallel cpc path) even with both ends disconnected at the distribution board.
Dunno, think the OP is saying no such heaters present?
Yep you could be right, perhaps the OP can confirm.Still think the RFC quite large, unless the whole property has only one RFC, or it's just big?Perhaps. But depending on what is connected and how (e.g. with dual boxes creating connections to other circuits' cpcs) it is possible for there to be parallel cpc paths, although not near as likely as on a job with steel containment obviously!
OP is saying he's testing at CU with ends disconnected, no appliances or loads connected.
Yeah I did see your post my friend, and of course agree, but don't think it is in relation in this case, good shout though, I accept your view if there would be a boiler in the circuit as you have suggested.See my earlier post. If the heating is a gas boiler and fed from the RFC, and the gas supply is bonded, this may be the parallel path?
Well in general tel is correct, I agree it isn't always the case but he has a point.Maybe not applicable to this case, but I was just replying to tel's implication that disconnecting the CPCs from the board would be enough to eliminate parallel paths when measuring r2 on a ring.
or dodgy connectionsAnother possibility, is that there is an RCD socket or perhaps an item of equipment connected which is skewing the results.
Out of curiousity what is the formula for calculating length of run? Cheers
OP says #21 that it is a new property, so we assume new wiring, so likely also new (possibly cheap) sockets which could be giving poor connection on L & N
I thought his reading was based on the end-to-end resistances, which wouldn't be affected by the socket contacts. Presumably the actual terminal screws are tight in the socket outlet.