Hi Everyone!
We build a 3 phase electric grill at my company.The grill has 6 elements.The elements are connected in delta, but..
4 elements work with a thermostat and 2 element work with an energy regulator.
So thermostat 4 elements connected:
L1-L2
L1-L3
L1-L2
L1-L3
Energy regulator 2 elements connected:
L2-L3
L3-L2
Also we have 3 led.Every phase have 1 led.
Phase 1 has the all 6 mini fan.
My problem is,i found 1 ampere on earth.If only energy regulator works with the 2 elements,no current flow to earth.Immediately i turn on the thermostat(4 elements) 1 ampere current flow to earth.
There is a 4 pole RCD what does not trip in this situation neither.
Neutral connected only to led and to fans.
There is no cross connection and the insulation resistances are all fine.
RCD disconnection time is fine and test button as well works.
My question is, how possible there is 1 amp on earth?
Why RCD does not trip?
Why i do not get electric shock if i touch the exposed metal part of the grill?

Thanks!!
 
Red in this case is neutral.I do not understand your question.So i share a picture.I clamped at both place(like on picture)
[automerge]1591102191[/automerge]
At first picture is 1 amp.at second more far from earth conductor is around 800 mA
 

Attachments

  • 20200602_134647.jpg
    20200602_134647.jpg
    93.6 KB · Views: 29
  • 20200602_134651.jpg
    20200602_134651.jpg
    59.2 KB · Views: 28

Reply to Earth current in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
As the holiday season approaches, PCBWay is thrilled to announce their Christmas & New Year Promotions! Whether you’re an engineer or an...
Replies
0
Views
740
  • Article
Bloody Hell! Wishing you a speedy recovery and hope (if) anyone else involved is ok. Ivan
    • Friendly
    • Like
Replies
13
Views
1K
  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
974

Similar threads

  • Question
I'm familiar with many domestic extractor fans which are primarily class 2 (double insulated) and consequently are not required to be earthed...
Replies
13
Views
2K
  • Question
Yes I touched on diverted neutrals when I went over guidance note 3 the first time but I’m doing a second round and going between all books whilst...
Replies
9
Views
628

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top