Hello.
I'm in the final stages of completing my electrician course, and I find myself confused (again) by EFLI.

In the textbook provided is this:

Uo 230V
see below for each circuit.

Calculate the maximum Zs for each circuit:
Complete the table.

The answers given in the textbook are said to be correct.

However, according to BS7671, the values in the textbook exceed the maximum allowed Zs.

Eg: For the outbuilding circuit, BS7671 states type B 20A has max Zs of 2.19 ohms, yet the book says the correct answer is 2.30 ohms?

Am I missing something here?
Please can anyone help with this?
Thanks,
Gary

[ElectriciansForums.net] Earth fault loop impedance - textbook values vs BS7671

[ElectriciansForums.net] Earth fault loop impedance - textbook values vs BS7671

[ElectriciansForums.net] Earth fault loop impedance - textbook values vs BS7671

[ElectriciansForums.net] Earth fault loop impedance - textbook values vs BS7671
 
Last edited:
Ok, issue sorted.
According to the tutors, the answers in textbook are prior to amendment 3 and even though the version textbook was printed”after” amendment 3, somehow it didn’t get updated too.

So after applying Cmin factor 0.95, it brought the answers down to where they should be!
 
even before amd 3 and Cmin. ( which is to allow for supply volts down to 218V ), correction factor for cable temperature was to allow for temp. to be 70 deg.C, i.e . a factor of 0.8. applied to the BS7671 tabulated figures.
 

Reply to Earth fault loop impedance - textbook values vs BS7671 in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
271
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
766
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
774

Similar threads

  • Question
It's the same with any system, if you put poo in, you get poo out!
Replies
4
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top