Hello.
I'm in the final stages of completing my electrician course, and I find myself confused (again) by EFLI.
In the textbook provided is this:
Uo 230V
see below for each circuit.
Calculate the maximum Zs for each circuit:
Complete the table.
The answers given in the textbook are said to be correct.
However, according to BS7671, the values in the textbook exceed the maximum allowed Zs.
Eg: For the outbuilding circuit, BS7671 states type B 20A has max Zs of 2.19 ohms, yet the book says the correct answer is 2.30 ohms?
Am I missing something here?
Please can anyone help with this?
Thanks,
Gary