In my book, that's the tabulated value it gives me
What book is that?
Follow along with the video below to see how to install our site as a web app on your home screen.
Note: This feature may not be available in some browsers.
Discuss Earth fault loop impedance in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net
In my book, that's the tabulated value it gives me
In the byb they have reduced the maximum zs values now so a b32 amp mcb was 1.44 is now 1.37 sorry i forgot the reason why , might be to do with Europe it normally is
What book is that?
What book is that?
its just one of the questions in my learning material. Its not a book.
Iv checked the official values online and none of them are the same as the tabulated values they have listed.
strange
Yes those are out of date as of last July. You can still answer the question perfectly well though, just don't learn your tabulated values from those sheets. Refer to your BYB for clarification.
feel shy to ask.....what is BYB?
thanks
so working with the tabulated values I'm given in my material would the formula I posted be the right way to go about it?
I am of the opinion that the course material is out of date as the Cmin factor of 0.95 is already worked into the new maximum values.
The question is simply asking for you to apply the temperature correction factor to the maximum values and compare those values with the given measured values and state whether compliant or not.
You could point out in your answer that the Cmin factor of 0.95 should be applied if you would like to illustrate you have been given out of date material.