In the byb they have reduced the maximum zs values now so a b32 amp mcb was 1.44 is now 1.37 sorry i forgot the reason why , might be to do with Europe it normally is

The Cmin factor is taken from CLC/TR50480:2011
 
Last edited:
What book is that?

its just one of the questions in my learning material. Its not a book.

Iv checked the official values online and none of them are the same as the tabulated values they have listed.

strange

They changed with the last edition of BS7671 which was published January 2015 and came into force last July. This introduced the new Cmin factor which dropped the maximum values to 95% of their previous value.

Your course material is out of date in that respect.
 
Last edited:
:-) thanks

so working with the tabulated values I'm given in my material would the formula I posted be the right way to go about it?

I am of the opinion that the course material is out of date as the Cmin factor of 0.95 is already worked into the new maximum values.
The question is simply asking for you to apply the temperature correction factor to the maximum values and compare those values with the given measured values and state whether compliant or not.

You could point out in your answer that the Cmin factor of 0.95 should be applied if you would like to illustrate you have been given out of date material.
 
I am of the opinion that the course material is out of date as the Cmin factor of 0.95 is already worked into the new maximum values.
The question is simply asking for you to apply the temperature correction factor to the maximum values and compare those values with the given measured values and state whether compliant or not.

You could point out in your answer that the Cmin factor of 0.95 should be applied if you would like to illustrate you have been given out of date material.

Yes I would like to do that :-)

seems negative learning material that is out of date
 
Best EV Chargers by Electrical2Go! The official electric vehicle charger supplier.

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

YOUR Unread Posts

Daily, weekly or monthly email

Thread starter

gazdkw82

Arms
-
Joined
Location
leicester
If you're a qualified, trainee, or retired electrician - Which country is it that your work will be / is / was aimed at?
United Kingdom
What type of forum member are you?
Electrical Engineer (Qualified)

Thread Information

Title
Earth fault loop impedance
Prefix
N/A
Forum
Periodic Inspection Reporting & Certification
Start date
Last reply date
Replies
25

Advert

Thread statistics

Created
gazdkw82,
Last reply from
gazdkw82,
Replies
25
Views
8,903

Advert

Back
Top