So here is the situation
22kV/415V delta-star transformer with neutral point earthed on secondary
Downstream breaker of transformer 630A with earth fault setting 0.2xIn @ 100ms
This supplues a number of outgoing loads with respective 50A breakers which only have thermal and magnetic settings.
An earth fault occurred downstream the 50A breaker tripping the 630A and damaging the feeder to the load.
Is it recommended to remove the earth fault or adjust it higher?