hi, folks, went out to a job today. Central Heating contract, guy has refused to do any work on the boiler due to " unacceptable Zs reading at boiler spur, >200ohms. checked with MFT and got a ZSreading of 347ohms. hmmm. goes to CU and it's 16th with 30mA RCD covering all circuits. bonding to gas and water connected and look OK. as a quick check, took a Ze reading ( 3 lead with all earths/bonding still connected, ) read 0.16ohms. then after shifting several boxes etc. to access main fuse, not TNC-S and not TN-S, incoming cable is plastic sheath, not lead, as i had originally supposed from the age of the property. OK, thinks, must be TT, so where's the rod? also, Zs on every circuit is around 350. earth cable disappears down through floor to cellar, now inaccessible, so before identifying and disconnecting bonding ( as there are 3 cables in earth bar, all 10mm, so can't tell which is main earth, i've come to the conclusion that it is TT and somehow this has been disconnected. i've quoted for fitting a rod ( accessible) with the proviso that further work may be necessary . question is why has the boiler guy refused to do a ssevice as on a TT system with RCD, any reading below 1667 is acceptable?