Sav
Hi everyone and a happy Easter to you all.
Got a call today to install a consumer unit for a customer into their brand new garage.
They had an electrician who run a swa from an isolator to the new garage board, but could not finish the job as "the earth has voltage guv and its illegal to connect up". Thats what he told the lady.
He has now gone out of business and is abroad ( so he told them).
Anyway, I checked the earth and true there is 40v present at the earth. I did insulation resistance which also confirmed the earth issue.
The thing is, the floor is now tiled over and flooring laid in the hallway ( the isloator is in a small kind of cellar, not very deep though ). I have run a 16mm earth from the isolator (just about got it through behind kitchen units but no way can you get swa there at all), along the garden wall, its in plastic conduit now and into the consumer unit. ZS,R1+R2 ok on the swa and also PFC and ZE ok from the consumer unit as well as sockets and lights (complete test carried out) .
Is this ok in your view, or is there anything else that I must or should do. ??? Even though all looks ok, I have left the isolator off and removed the fuse until feedback from you guys.
Setup is as follows:
60amp d/pole isolator BS1361
16mm swa
original 16mm earth now is safely terminated into a block with brown tape and a note in front of isolator explaining situation (same at consumer unit).
Thanks and regards,
Sav
Got a call today to install a consumer unit for a customer into their brand new garage.
They had an electrician who run a swa from an isolator to the new garage board, but could not finish the job as "the earth has voltage guv and its illegal to connect up". Thats what he told the lady.
He has now gone out of business and is abroad ( so he told them).
Anyway, I checked the earth and true there is 40v present at the earth. I did insulation resistance which also confirmed the earth issue.
The thing is, the floor is now tiled over and flooring laid in the hallway ( the isloator is in a small kind of cellar, not very deep though ). I have run a 16mm earth from the isolator (just about got it through behind kitchen units but no way can you get swa there at all), along the garden wall, its in plastic conduit now and into the consumer unit. ZS,R1+R2 ok on the swa and also PFC and ZE ok from the consumer unit as well as sockets and lights (complete test carried out) .
Is this ok in your view, or is there anything else that I must or should do. ??? Even though all looks ok, I have left the isolator off and removed the fuse until feedback from you guys.
Setup is as follows:
60amp d/pole isolator BS1361
16mm swa
original 16mm earth now is safely terminated into a block with brown tape and a note in front of isolator explaining situation (same at consumer unit).
Thanks and regards,
Sav