^^Yeah deffo not a voltage operated device. The set up above is pretty much standard for large domestic and small commercial, we don't usually use pre-assembled CU's and I'm surprised there's even busbar, usually the MCB's etc just have multiple wire links across the tops of them.
Not sure why it's a 3-phase supply, domestic is usually single phase 60A but wit three geysers it's possibly commercial. The fixed loads such as geyser (immersion heater) and also the outbuilding should be fed by d/pole SP+N MCB's so the DB is not compliant.
JSpark, the board is a bit rough even by our standards but par for the course. Refer to the previous posts, identify the L+N of all the circuits on the RCD and do the tests for insulation and crossover with other circuits. Just be methodical, treat as dangerous until you figure out why the earth leakage is tripping with the main breaker off.
Not sure why it's a 3-phase supply, domestic is usually single phase 60A but wit three geysers it's possibly commercial. The fixed loads such as geyser (immersion heater) and also the outbuilding should be fed by d/pole SP+N MCB's so the DB is not compliant.
JSpark, the board is a bit rough even by our standards but par for the course. Refer to the previous posts, identify the L+N of all the circuits on the RCD and do the tests for insulation and crossover with other circuits. Just be methodical, treat as dangerous until you figure out why the earth leakage is tripping with the main breaker off.