I'm not a sparky. I have two houses on my plot (not in England) and the small house takes a mains feed from the main house and has its own consumer unit. For some reason we get little shocks from things like computer cases from anything connected to the second consumer unit.

We do not have the second consumer unit earthed - will this likely be the problem ?
 
Sounds very much like an earthing problem to me if it was just the computer cases it might be just static however you say everything. Whats your nearest town perhaps someone on the forum can pop round and ensure everything is safe and put your mind at ease.


Chris
 
If you have no earth to 2nd consumer unit this is most probably the cause as any earth fault current has nowhere to go.

You need to run an earth to cu and all associated circuits and preferably install additional protection by 30mA RCD.
 
Thanks you Guys. Chris has got me wondering if it is only devices connected to the computer that are a problem. I will have to ask my son, who is the one that gets lit up all the time.

perhaps someone on the forum can pop round and ensure everything is safe and put your mind at ease.
:D I don't think so Chris - I live in Thailand..... but if you're ever passing :cool:
 
Not had any experience myself of one CU fed off another. Would there not be an earth (as well as the lives) between the CUs? So therefore the second one would effectively be earthed? I know in this case we're talking Thai electrics, but I am asking about in the UK.
 

Reply to Earth Leakage in the Australia area at ElectriciansForums.net

Similar Threads

  • Question
Just an update for anyone interested, I got another rod in outside today, which has lowered the Zs db to a more healthy 53ohms. The oven elements...
Replies
19
Views
3K
  • Question
I think there is a little truth in what the guy in the video says, but he makes more out of it than he should. A N-E fault on a circuit protected...
Replies
28
Views
1K
  • Solved
There is an article about that here: https://www.cement.org/learn/concrete-technology/durability/corrosion-of-embedded-materials It states...
2
Replies
27
Views
2K
Hence the former name for TNC-S, PME. Protective Multiple Earth.
Replies
5
Views
618
Electric hob/oven range was installed years ago, runs on 2 x B32 MCBs to 'House' (sub)consumer panel, runs to oven on 2 x T&E. Kitchen is being...
Replies
0
Views
211

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock    No Thanks