We have measured 50mA earth leakage from an oven.but during we touch the metal surface we do not receive shock how?
Follow along with the video below to see how to install our site as a web app on your home screen.
Note: This feature may not be available in some browsers.
Discuss Earth leakage in the UK Electrical Forum area at ElectriciansForums.net
What do you mean exactly?i am confused.That's what should happen
An electric shock shouldn't happen regardless of leakage when all is well
So those 2 facts imply the reading is inaccurateWhat do you mean exactly?i am confused.
Also the oven is RCD protected and it does not operate.RCD is tested an work well.
Between lines and neutral.its 3 phase.we have measured with earth leakage clamp meter.the best think is,we did with 2 differen clamp meter but we obtained the same results.How are you measuring the leakage and what with
You clamped all the live conductors ?Between lines and neutral.its 3 phase.we have measured with earth leakage clamp meter.the best think is,we did with 2 differen clamp meter but we obtained the same results.
Yes i clamped all lives.RCD has been tested for disconnection time.also the functional test button.You clamped all the live conductors ?
Did you test the rcd or push the button ?
Yes it isIs this a 30mA RCD?
Earth leakage clampmeter.What tester have you used?
Which one though? Some cheaper ones are incredibly inaccurateEarth leakage clampmeter.