ok so for the people who seem not to know where the values come from. 21 ohms is the value that your local supply authority quote for the earth value at the their substation if you put a rod down there. this is not the reading you are trying to achieve. 1666ohms , this is the reading you need to achieve to stop a touch voltage of 50volts occurring when using a 30ma rcd. 50v/0.03A=1666ohms. also if you are using a 100ma then it would be 50/0.1=500ohms. the reading of 200ohms is the level that is deemed to be a stable reading, however a reading slightly above this as with the original post is neither here or there. you are not relying on the earth rod to operate an mcb, hence why you "have" to use rcds on all circuits on a tt system. the mcb is there to protect the circuit from overload only, in tt case this will be phase to neutral. and when the fault is to earth the rcd is the means of protection to the operator and not to the cable. so the reg of "do not use a rcd as sole means of protection" would mean you do not have a bank of rcds and no mcbs. this is where you use rcbos. so with all this in mind you as the electrician need to use some common sense and decide if you are happy with the reading. if you put in a brand new rod and get a reading of 220ohms then I would deem that as a stable reading. if it was an old bit of corroded water pipe giving a reading of 220ohms, then I would say that it should be replaced with a new rod. both surface area and depth are the factors to improve the reading. but there will be a minimum reading you will not get below as this is the resistance of the earth and substation earth rod.I hope this is of help. andy
 
lol ok but i have worked on a few tt systems and a longer rod buryied deeper usualy will bring the resistance down, i cant think of any other way that will

If it's not wet enough already then chuck a hose on it for an hour or two and then re-test! Seriously though, the only way you will reduce the impedance reading is to lengthen the electrode, but where do you stop? :)
 

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Green 2 Go Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

YOUR Unread Posts

Daily, weekly or monthly email

Thread Information

Title
Earth Loop Impedance on a TT system
Prefix
N/A
Forum
Electrical Wiring, Theories and Regulations
Start date
Last reply date
Replies
57

Advert

Thread statistics

Created
roukel01,
Last reply from
D Skelton,
Replies
57
Views
16,665

Advert

Back
Top