OP
PEM
I work on TT a lot in the depths of Suffolk/Norfolk. I'd recommend a longer rod in addition to the existing. I've even used 3 to bring Readings down to acceptable levels.
Regards
Regards
Follow along with the video below to see how to install our site as a web app on your home screen.
Note: This feature may not be available in some browsers.
Discuss Earth Loop Impedance on a TT system in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net
The problem you have encountered is a common scenario and sticking rods in deeper and deeper is generally not the answer. As you have stated the reading is at this value when ground saturated and will rise when ground dries (Summer). A 30mA rcd will work upto a Zs of 1666.66 ohms but obviously a value below 100 ohms would be what i would be expecting. Look at Furse who are the earthing mat specialists. They make a copper matt approx 1 meter square which when buried to a depth of a meter (dependant on ground) will drop earth reading. Generally i can obtain between 33 and 80 ohms in poor conditions.
21 ohms is the value of the DISTRIBUTORS earth electrode at the supply transformer , 200ohms is the maximum value of the CONSUMERS earth electrode (which is the one I'm talking about)
As my first post said, I'm asking folks who have experience in this, if a longer rod would bring the result down enough, or if another method my be needed.
It is given in the introduction of the OSG as the maximum stated resistance!Where did you get that figure for supply transformers from?
Afternoon all,
I did a standard Ze test on a TT installation yesterday, and got a value of 215 ohms. The ground is really wet at the moment and so I'm assuming its about as good as the rod is going to get.
Would simply replacing the rod with a longer type improve the Ze result? and if not, what methods are best to reduce the result?
Many Thanks.
The problem you have encountered is a common scenario and sticking rods in deeper and deeper is generally not the answer. As you have stated the reading is at this value when ground saturated and will rise when ground dries (Summer). A 30mA rcd will work upto a Zs of 1666.66 ohms but obviously a value below 100 ohms would be what i would be expecting. Look at Furse who are the earthing mat specialists. They make a copper matt approx 1 meter square which when buried to a depth of a meter (dependant on ground) will drop earth reading. Generally i can obtain between 33 and 80 ohms in poor conditions.
As i am sure you are well aware 2*5/8ths rods no doubt will reduce the earth loop impedance value but think you are grasping at straws. A 'Furse' copper lattice mat will have at least 20 to 30 times the conductive surface area to ground than rods. This is what is required to lower resistivity. Sorry but you are mistaken in this matter.So you think a 1m square latice mat at a depth of 1m will be better than a deep driven rod do you, ....somehow I don't think so!!
He's more than probably got a thin twig as his earth electrode Which are the next best thing to being totally useless and more likely than not, positioned right next to an external wall of the house where all the old building rubbles is going to be!!
He's best bet, is to use at least 2 X 5/8'' rods coupled together for stability and a much improved Ra value!! Positioned at least 1.5m away from any external house walls. If the ground has a poor conductive value then there are soil conditioners that can be applied, that can/will also lower Ra values....
Interesting that once again people seem to think that 'between 33 and 80 ohms' is the dogs danglies....whats 33-80 ohms going to do that 215 wont?
Anyway....:nonod:
.......Regarding the OP.....I had a rod on an EICR recently on a separated earth on a small sewage plant with an Ra of 700+ ohms. Two coupled 4ft rods and it went down to around 13.....so there's your answer.
(that said though whats 13 ohms going to do that 700 wont in practice....a 30ma rcd will trip just the same on both readings,the OCPD will not trip on either reading)
Interesting that once again people seem to think that 'between 33 and 80 ohms' is the dogs danglies....whats 33-80 ohms going to do that 215 wont?
Anyway....:nonod:
.......Regarding the OP.....I had a rod on an EICR recently on a separated earth on a small sewage plant with an Ra of 700+ ohms. Two coupled 4ft rods and it went down to around 13.....so there's your answer.
(that said though whats 13 ohms going to do that 700 wont in practice....a 30ma rcd will trip just the same on both readings,the OCPD will not trip on either reading)
I fully agree that the Rcd will trip on both 33 to 80 ohms and also 215 ohms but do not understand the arrogant remark ' dogs danglies'. Maybe better to give this a little further thought. Why is 33 to 80 better than 215 ohms ?. Maybe this will give an increased assurance that electrode will not rise above acceptable levels. Do not wish to get in to slagging match over this. Designing and installing these on a regular basis. Earth lattice matt over earth electrode will win hands down every time.
Reply to Earth Loop Impedance on a TT system in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net