Hi guys, i after some help with an Earth Loop question, first thing first this is not coming from a sparks prospective so the regulations are not relevant here to a point.
I work in the domestic appliance industry, i contract to one of the big manufactures, as part of our initial tests on the equipment such as earth continuity and Insulation resistance we perform a no trip earth loop test, out testes first confirm the socket wis correctly wired and that an earth is present, then we perform the test, we are to regardless of the system e.g. TT,TNCS, TNS a reading of 200ohm or below is acceptable for out point of view, over 200 and we issue an notification of a possible issue with the system.
because we have no legal requirement of the installation is self we are testing to ensure the socket we are connecting the appliance to is safe for the engineer to work on and should there be an issue protection devises (RCD/MCB) will trip.
Now here is where the issue is, in discussions with other engineers of various skills some understand more than others some are concerned that 200ohm is wholly inadequate and down rite dangerous, its been pointed out that at 200ohm you would only get fault current of 1A, not enough to trip a 32a mcb, if the is an RCD then its fine BUT its no non RCD we are concerned about.
now i have been doing electrical maintance for over 10 years, i did my 2330 years ago but not been deeply involved with installation for years.
the Manufactures have set a blanket reading to make it easier on the engineers and they must have come up with this for a reason
am i missing something here?
I work in the domestic appliance industry, i contract to one of the big manufactures, as part of our initial tests on the equipment such as earth continuity and Insulation resistance we perform a no trip earth loop test, out testes first confirm the socket wis correctly wired and that an earth is present, then we perform the test, we are to regardless of the system e.g. TT,TNCS, TNS a reading of 200ohm or below is acceptable for out point of view, over 200 and we issue an notification of a possible issue with the system.
because we have no legal requirement of the installation is self we are testing to ensure the socket we are connecting the appliance to is safe for the engineer to work on and should there be an issue protection devises (RCD/MCB) will trip.
Now here is where the issue is, in discussions with other engineers of various skills some understand more than others some are concerned that 200ohm is wholly inadequate and down rite dangerous, its been pointed out that at 200ohm you would only get fault current of 1A, not enough to trip a 32a mcb, if the is an RCD then its fine BUT its no non RCD we are concerned about.
now i have been doing electrical maintance for over 10 years, i did my 2330 years ago but not been deeply involved with installation for years.
the Manufactures have set a blanket reading to make it easier on the engineers and they must have come up with this for a reason
am i missing something here?