we have had installed some Hagar ARM932U Arc Fault Detection Device in one of our care homes.
they had reported tripping issues , so i tried to do an (RCD) Residual Current Device test.
it wont trip at any current.
looking it up it seems they are not also an rcbo . if so whats the point of them.
also if so they should not have been installed i think
has anyone else come across similar issues?
i have contacted Hagar for confirmation.
 
has anyone else come across similar issues?

Watch the David Savery video's on YT he has done a few on AFDD's and also a rift with Hager.

ARM932U is the MCB model

ARR932U is the RCBO model

Possibility the wrong one was ordered? Though the MCB model is a double module so would have thought that would have flagged it.
 
thanks for the confirmation this is what i thought.
i cant think of what use this device is .
i have seen David Saverys Arc Fault Detection Device testing videos most interesting
 

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

newfutile

Arms
Supporter
-
Joined
Location
hemel hempstead
If you're a qualified, trainee, or retired electrician - Which country is it that your work will be / is / was aimed at?
United Kingdom
What type of forum member are you?
Electrical Engineer (Qualified)

Thread Information

Title
Hagar AFDD problem
Prefix
N/A
Forum
UK Electrical Forum
Start date
Last reply date
Replies
4

Advert

Thread statistics

Created
newfutile,
Last reply from
newfutile,
Replies
4
Views
787

Advert

TrueNAS JBOD Storage Server

Back
Top