W

woodbutcher32

Morning all, I'm in the process of selling my house and an inspection by a local electrician has thrown up several queries, any help & advice would be greatly appreciated...

"No existing main earth to incoming water"- Is it possible for me to simply install another Earth rod or MUST I go back to the CU (Which would be complicated)

"Existing earth to earth rod has no mechanical protection" - Is this just a case of enclosing the earth from the CU to existing front earth rod in plastic conduit?

"Existing lighting circuits are not looped in and a continuity of earth cannot be verified" he is advising re-wiring 8 no. lights (3 of which are 2 way) Is this really necessary or is there an alternative? The wiring in the house was re-wired around 10 years ago and is all in good condition, the cost he is quoting is money that I don't realy have!

"consumer unit has exposed parts" he is advising replacing with a new 17th. edition CU but is this really necessary by law?

thanks again

Woody
 
Morning all, I'm in the process of selling my house and an inspection by a local electrician has thrown up several queries, any help & advice would be greatly appreciated...

"No existing main earth to incoming water"- Is it possible for me to simply install another Earth rod or MUST I go back to the CU (Which would be complicated)
There is no such thing as "earthing the water main".....I assume he means main bonding,which calls into question the competance of the inspector if he cant use the correct terminology.....Main bonding is nothing to do with earthing but is essential,and MUST be run from the incoming point of entry (stop cock) to the MET
"Existing earth to earth rod has no mechanical protection" - Is this just a case of enclosing the earth from the CU to existing front earth rod in plastic conduit?
Probably the electrode itself,protective boxes are available to protect the connection and make the rod visible.

"Existing lighting circuits are not looped in and a continuity of earth cannot be verified" he is advising re-wiring 8 no. lights (3 of which are 2 way) Is this really necessary or is there an alternative? The wiring in the house was re-wired around 10 years ago and is all in good condition, the cost he is quoting is money that I don't realy have!...No idea what he means...very vague.

"consumer unit has exposed parts" he is advising replacing with a new 17th. edition CU but is this really necessary by law?
Probably an old rewirable wylex,in which shielding of live parts was a little suspect....you are no under any obligation in law to do any remedial work to your house,it is only a recommendation.
thanks again

Woody
................................
 
Presumably you are a TT system and as such the main earth must go from the CU or the MET directly to the earth rod.

Existing earth has no mechanical protection - you could sort this when you do the first point.

There is no regulation that is retrospective concerning CPC's on the lighting circuit. You should note that that use of class 1 fittings (if you have any) should be removed.

Consumer unit has exposed parts - can you post a picture? Yes, a replacement CU may be ideal but may not be necessary.
 
Many thanks for the replies so far I'll get some pics up later today! Thanks wirepuller, what i mean is the gas is already 10mm earthed to the CU then from the CU to an earth rod, is it possible for me to simply install another earth rod at the rear of the property and 10mm cable straight to that from the water main?
Sorry if my terminology is a little vague but im a Carpenter by trade!
 
Last edited by a moderator:
If the gas and the water main are in the same proximity, you can link the two services on that single 10mm cable. However, it's always advisable to run separate main bonding conductors.

There is nothing to stop you running the water bonding cable around the house, attached to the fabric of the house. But it would be sensible to afford it mechanical protection. My choice would be plastic (PVC) conduit.

Just to clear things up a little, ''class 1'' light fittings are light fittings requiring and earth connection, ''Class 11'' light fittings, are fittings that are double insulated and do not require or have an earth connection incorporated within.
 
"Existing lighting circuits are not looped in and a continuity of earth cannot be verified"

This is open to interpretation, is the sparks expecting the lighting to be done as a ring? Or just can’t be bothered to look in the fittings?

What ever the cause I think it was a case of scare tactics to force our OP in to unnecessary work. my thoughts are the same for the CU
 
You have said that it was rewired 10 years ago i would find in strange that the consumer unit was not changed,and that the main earth bonding to the water service was not in place,it may have been connected to a place where the inspector did not check,and if it was rewired at that time did they supply an installation certificate,these are things that i would ask about as soon as starting an inspection,its all about gathering information and compiling a report,legally you are not obliged to change a thing,the only consequence is that the potential buyers will try and knock you down on price,pictures on here would help us guide you better.
 
Morning all, I'm in the process of selling my house and an inspection by a local electrician has thrown up several queries, any help & advice would be greatly appreciated...

Always an interesting scenario, If I were buying a house and the electrics looked old then ÂŁ5k comes off the asking price straight away, the same with CH and boilers.... something to bear in mind when you get offers below what you were expecting
 
Many thanks for all the advice thus far

This is a pic of the currently installed CU unit, what changes would have to be made to pass an electrical cert?



[ElectriciansForums.net] Earth Queries (+ others!)
 
Many thanks for all the advice thus far

This is a pic of the currently installed CU unit, what changes would have to be made to pass an electrical cert?

If that up front RCD is 30ma no changes are essential. A single RCD protecting the whole installation does not comply with the regulations as a fault on one circuit will trip the whole system,however this would not necessarily result in an unsatisfactory report.
If the RCD is not 30ma (100ma?)...then socket outlets would not be 30ma RCD protected and on a TT system this would result in an unsatisfactory report. The push button MCB,s are no longer a recognised overcurrent device,but can easily be changed.
Of course it's crying out for updating,but not essential.





View attachment 8011
..........
 
Last edited by a moderator:

Reply to Earth Queries (+ others!) in the Australia area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
332
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
859
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
983

Similar threads

  • Question
One of those backlight Chinese testers may have helped that’s if the tester didn’t catch fire or electrocute you. LED TV Backlight Tester 12W LED...
2 3 4 5
Replies
68
Views
4K
In my opinion replacing the consumer unit and waiting to see which RCBO trips is not a good fault finding technique. If the lighting circuit...
Replies
8
Views
687
davesparks
D

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top