I need to run several new supplies for studios. 16mm T&E is fine for the supplies. But I'm worried the earth may not be big enough. Longest run is 12M from Meter. I could just run cable then if it fails test run 16mm earth. But would be interested to learn the calculation so I can be sure from the outset.

Thanks
Michael
 
SWA adds about £150, although could use 2 core and armour as earth for only small increase in cost. Had not thought about RCD for supply cable. I thought this was only a requirement for sockets. What would make this install require RCD on supply cable?

Earth is TN-S

Need to get my head round adiabatic
 
Just a thought, if I only need 60A to each studio I can use 16mm T&E. Similarily I could run 6mm 2 core SWA. Assuming minimum 10mm earth required, how big would armour work out to be on 6mm SWA ?
Would also need to look at voltage drop, but thinking out loud.
 
But isn't that just for sockets, you don't need this for lights, so why for supply?

The regs in this case apply to all power cables, submain, lighting switch drops, sockets, cooker. All cables require rcd protection if buried in a wall less than 50mm deep, unless they are suitably protected (metal conduit, armoured cable etc)
 

Reply to Earth Requirement in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
330
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
855
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
975

Similar threads

  • Question
This charger doesn't support rear entry from the looks, only bottom entry, hence that. Unless they make a white sheathed SWA, I would still need...
Replies
8
Views
1K
If the shared neutral is lost ,won`t you be getting 400v across both cottages? 2 phase US style but double the Voltage.
Replies
22
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top