hi to all
when asked for external earth return path for a TT system is it
General mass of earth
Supply earth electrode

For TN-C-S system is it
supply PEN conductor

for TN-S
supply protective conductor
thanks
 
its earthed through
1 consumers earth electrode
2 general mass of earth
3 supplier earth electrode

the question asks earth path external to installation so it cant be number1 as belongs to installation

i also have one that says earth fault path extaernal to istallation
and tutor at college says
TT . General mass of earth
supplier earth electrode
star point
secondary winding
supply lines
supply overcurrent protective device

TN-S
supply protective conductor
star point
secondary windings
supply line
supply overcurrent protective device

TN-C-S
PEN conductor
star point
secondary windings
supply line
suppliers overcurrent protective device

thats why i think earth return path for a tt is
General mass of earth
Suppliers earth electrode
 
Last edited:
Upvote 0

Reply to earth return path in the Electrician Courses : Electrical Quals area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
438
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
1K
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

In TN-S systems, you shouldn't isolate the neutral in a 4-pole isolator. Connecting neutrals to a dedicated terminal is acceptable and safe...
Replies
4
Views
673
It's not the same scenario, though. Tails more than 3mtrs can be overcome by using a fused switch and rcd board, whether the earthing system is...
2
Replies
18
Views
827

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

Electrical Courses

This is the main Electrical Courses at ElectriciansForums.net. Find local recommended electricians courses. Avoid training "company" scams. Always go view the training centre before booking any electrical courses.
This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top