Dillb mateSo you are happy leaving metal work that is carrying cables not to be bonded back to the MET?
Explain how that is dangerous and not a safety connection then please?
Yes i am happy leaving metal work that is neither extraneous or exposed conductive parts unbonded/earthed. just like when i have put up double insulated metal fittings, with BS and the double square markings i have not decided to earth them to be on the safe side
heres why
Exposed-conductive-part.Conductive part of equipment which can be touched and which is not normallylive, but which can become live under fault conditions.
Extraneous-conductive-part. Aconductive part liable to introduce a potential, generally Earth potential, andnot forming part of the electrical installation
A cable tray or a cable basketwhere used as a support and cable management system has to be considered in thecontext of earthing and bonding. In other words, are such systems, whereconsisting of metal and plastic-coated metal, exposed-conductive-parts orextraneous-conductive-parts and consequently do they require earthing orbonding?
Addressing, first, the questionof earthing and whether the cable tray or basket should be earthed, electricalequipment such as cables mounted on a metallic support system will normally beequivalent to either a Class I construction (for example copper sheathed,mineral insulated cables without an overall PVC covering) or a Class IIequivalent construction (for example PVC insulated and sheathed cable).
Exposed-conductive-parts ofcables, such as the copper sheath of a mineral insulated cable, are required tobe connected to the MET of the installation by a CPC designed to conduct earthfault currents. The cable tray or basket which the mineral insulated cable isattached to, or may be in contact with, is not itself anexposed-conductive-part and therefore it does not require earthing. To do sowould only serve to distribute further any touch voltage resulting from anearth fault on an item of equipment to which the cable is connected.
A cable complying with theappropriate standard having a non-metallic sheath or a non- metallic enclosureis deemed to provide satisfactory protection against both direct and indirectcontact, as does an item of Class II equipment (Regulation 471-09-04 refers).Class II equipment is constructed such that any insulation fault in the cablecannot result in a fault current flowing into any conductive parts with whichthe equipment may be in contact. Hence, the metal cable tray or basket need notbe earthed