The main problem here, is that there are always stray neutral (and to some extent earth-fault) currents present in the ground. The objective is to reduce the risk that these currents pose to livestock such as horses and cattle (also to a lesser extent sheep and goats).
Use of an earth rod where such livestock are present is not advisable. The preferred method would be to install an earthed metallic grid. This would reduce the likely hood of there being 'step voltages' present.
Not happy that the SWA and CPC are earthed at the supply end.
To my mind, this means the TNC-S earth has been exported along the length the cable. Depending upon how and where the cable is run, there is a possibility that difference in potential could be introduced between the TNC-S earth and the earthing for whatever the cable supplies.
A 100mA or 300mA upfront RCD, is quite acceptable, though as has been already stated circuits that supply socket-outlets would require 30mA RCD protection.
It may also be advisable to provide 30mA RCD protection for other circuits.
Use of an earth rod where such livestock are present is not advisable. The preferred method would be to install an earthed metallic grid. This would reduce the likely hood of there being 'step voltages' present.
Not happy that the SWA and CPC are earthed at the supply end.
To my mind, this means the TNC-S earth has been exported along the length the cable. Depending upon how and where the cable is run, there is a possibility that difference in potential could be introduced between the TNC-S earth and the earthing for whatever the cable supplies.
A 100mA or 300mA upfront RCD, is quite acceptable, though as has been already stated circuits that supply socket-outlets would require 30mA RCD protection.
It may also be advisable to provide 30mA RCD protection for other circuits.