Iv been told you need to install a earth rod to earth array when using transformerless invertors ,seems a bit ott rcd not enough ?
Follow along with the video below to see how to install our site as a web app on your home screen.
Note: This feature may not be available in some browsers.
Discuss earth rod for TL invertors in the Solar PV Forum | Solar Panels Forum area at ElectriciansForums.net
Yes Josh apparently its true, (see the ‘array frame earthing decision tree’, in the DTI guide), but you only need to do this if it’s a PME supply. Use 10mm. Good luck
class a rcbos for pulsed dc for transformerless TL inverters to stop dc leaking into the grid
as these have no galvanic separation , HF range has transformers fitted but yields are lower
per esc guidelines i have supplied these for over two years now
also plug in grounding kits if hybrid sanyos or thin film panels are used
Not strictly true. If PME then earth stake array in 10mm earth, If TNS or TT then earth bond array back to MET in this case the size of bond cable must be equal size to bonding conductors already installed to the water, oil, gas etc.
Thanks very much ,must read DTI guide more often.Yes Josh apparently its true, (see the ‘array frame earthing decision tree’, in the DTI guide), but you only need to do this if it’s a PME supply. Use 10mm. Good luck
esc guidelines on transformless inverters recommend class a not class b rcds