Hi all
Having to install a earth rod In for a hot tub, hot tub just installed outside the house. I am planning on installing earth rod 100mm from edge of house what are the chances that there will be services below this line. The gas pipe and water pipe are further along the wall about 2M away I wouldn’t think the pipes will be running right along side the house would they ?
 
too close to house. allsorts of builders crap there. 1m min. from house. and then suss out where other services are. what reason needed for rod?
 
Well it was previously a hire hot tub came with a 13amp plug top but looking at spec says 16amp supply required and they are from Spain ?
last thing tat came from Spain was squashed by Drake. 1588.
 
If you are worried and have the patience then hand-dig down by 1m or so like putting in a fence post and then if no services it is unlikely to be below that, so then a long rod (2m or so) can be driven in and back-filled with the soil that came out.
 
This site will do a search for you for free, though you need to sign up and give the area details. Won't catch everything but at least gas mains and HV cables will be shown:

Give some margin around them as not all services are quite where the map shows them to be.
 
I have looked for info regarding earth rod but no luck with it just says 16amp supply. But would have thought hot tub would be better on TT earthing system anyway ? Don’t think it’s good idea having it on TNCS . I’ll just dig down about 600mm should be clear of all services in my garden then ?
 
I have looked for info regarding earth rod but no luck with it just says 16amp supply. But would have thought hot tub would be better on TT earthing system anyway ? Don’t think it’s good idea having it on TNCS . I’ll just dig down about 600mm should be clear of all services in my garden then ?
And if the network neutral develops a fault potentially your rod will be the only path for the neutral currents from your installation and possibly your neighbours back to the transformer.
 
But would have thought hot tub would be better on TT earthing system anyway ? Don’t think it’s good idea having it on TNCS
Some manufacturers do say it should be TT'd.

Here are some rambling disorganised thoughts: (EDIT related to just leaving it TNCS)
Extraneous metalwork from the house should be already dealt with, otherwise even before the hot tub arrives there's a problem.
The houses equipotential zone would be extended to a 16A socked on an external wall.
The hot tub probably doesn't have any exposed conductive parts as is effectively a double insulated plastic class II item.

What could go wrong...
-cable supplying it could lose earth connection + fault conditions + exposed conductive part (unlikely 1st two at same time, and most hot tubs wouldn't have 3rd)
-broken PEN on supply and all earthed conductors become live (hot tub probably class 2, safe inside it and around it, dangerous if you can touch a garden tap but that applies anyway)
-neutral return currents could be near buried extraneous conductors causing tingle - (GN7 advocates applying section 702 to outdoor hot tubs which would include earthing mat to tackle this ). Unless hot tub is a good distance away from building and any extraneous parts and the earth rod wouldn't help much
Have I missed anything?
 
Some manufacturers do say it should be TT'd.

Here are some rambling disorganised thoughts: (EDIT related to just leaving it TNCS)
Extraneous metalwork from the house should be already dealt with, otherwise even before the hot tub arrives there's a problem.
The houses equipotential zone would be extended to a 16A socked on an external wall.
The hot tub probably doesn't have any exposed conductive parts as is effectively a double insulated plastic class II item.

What could go wrong...
-cable supplying it could lose earth connection + fault conditions + exposed conductive part (unlikely 1st two at same time, and most hot tubs wouldn't have 3rd)
-broken PEN on supply and all earthed conductors become live (hot tub probably class 2, safe inside it and around it, dangerous if you can touch a garden tap but that applies anyway)
-neutral return currents could be near buried extraneous conductors causing tingle - (GN7 advocates applying section 702 to outdoor hot tubs which would include earthing mat to tackle this ). Unless hot tub is a good distance away from building and any extraneous parts and the earth rod wouldn't help much
Have I missed anything?
prophet of doom strikes again,. just plug it in, don't use mains radios and hairdryers in the tub. ensure sunlife policy up to date,
[ElectriciansForums.net] Earth Rod install
 
Some manufacturers do say it should be TT'd.

Here are some rambling disorganised thoughts: (EDIT related to just leaving it TNCS)
Extraneous metalwork from the house should be already dealt with, otherwise even before the hot tub arrives there's a problem.
The houses equipotential zone would be extended to a 16A socked on an external wall.
The hot tub probably doesn't have any exposed conductive parts as is effectively a double insulated plastic class II item.

What could go wrong...
-cable supplying it could lose earth connection + fault conditions + exposed conductive part (unlikely 1st two at same time, and most hot tubs wouldn't have 3rd)
-broken PEN on supply and all earthed conductors become live (hot tub probably class 2, safe inside it and around it, dangerous if you can touch a garden tap but that applies anyway)
-neutral return currents could be near buried extraneous conductors causing tingle - (GN7 advocates applying section 702 to outdoor hot tubs which would include earthing mat to tackle this ). Unless hot tub is a good distance away from building and any extraneous parts and the earth rod wouldn't help much
Have I missed anything?

I believe most have metallic heating element housing which are earthed meaning there is a chance the water can rise in potential should a PEN fault occur, although depends on the conductivity of the water and distance to the heating element to dictate how bad the concicences are

Yes earth mat under and around the hot tub i think is the best way connected to the TN-C-S earth , if i was to put one at my house I would go that way, although its a different story if you told a client you need to dig up a massive section of there garden to install an earth mat not sure how well that would fly
 

Reply to Earth Rod install in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
381
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
961
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

  • Question
Thanks for that guys I was more thinking about difference in potential between the tub and wet paving flags . The tub is plastic . But it’s the...
Replies
7
Views
2K
  • Solved
There is an article about that here: https://www.cement.org/learn/concrete-technology/durability/corrosion-of-embedded-materials It states...
2
Replies
27
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top