Hi all,

I'm having a car charger fitted in the next 2 weeks and the installer has mentioned they shall be fitting an earth rod.

I'm not too concerned as I'm sure these guys know what they are doing! However, I wondered how they will drive a rod into the ground whilst avoiding utilities, etc.

Also, the rod looks like it's going in near a gravel patch, so how would other professionals install a rod, would you drill a hole into the ground then hammer it or is there a tool needed to drill a rod into the ground.

Thanks!
 
You can drive it in with a drill but this is not best practice in-line with H&S legislation.

We hand dig with GRP fence post spades and CAT scan every 300mm.

Increasingly we are installing earth mats but these require a little more skill and expense to work with. The advantages is only need to dig to 350mm. The disadvantages is need to dig a square 1000x1000 and cost more.
 
Personally CAT scan around the area usually 1m² where the rod is going and put first 1.2m rod in with sledgehammer then the others on top with Hilti te1000 with earth rod attachment
 
Looks like i am going to be busy with all these CAT scans.;)

A doctor tried to replace his living room light, but kept blowing the fuse. He called an electrician, The electrician arrived, unpacked his tools, looked at the light and said “Ah! The old all the reds and blacks together ploy!” He sorted the wiring and handed the doctor a bill for £500.
The doctor exclaimed, "This is ridiculous! I don't even make that much as a doctor!."
The electrician quietly answered, "Neither did I when I was a doctor."

[ElectriciansForums.net] Earth rod installation
 
Personally CAT scan around the area usually 1m² where the rod is going and put first 1.2m rod in with sledgehammer then the others on top with Hilti te1000 with earth rod attachment

That's interesting. Thanks for that

If the earth is hard and dry would you tend to water it and knock in? Or would you go straight to knocking it in with the SDS / Hilti?

Also, isn't this bloody dangerous! It seems to me it's required due to the risk of losing the incoming Neutral but I've never heard of an example of this happening in the UK?

What if you have a bloody block paving drove etc.!
 

Thanks for that. Really interesting.

Isn't it more often than not a TNCS?

Very rarely a TT and same for TNS?

I just can't get my head around the risk with driving rods into the ground and not knowing for sure where any itilieuti are lay!
 
It seems to me it's required due to the risk of losing the incoming Neutral but I've never heard of an example of this happening in the UK?

What if you have a bloody block paving drove etc.!

This does happen, especially in the joint boxes under pavements which tap off and feed each house on the street.

Block paving is neither here nor there -if a rod is needed then a rod is needed. Block paving would need to come up.
 
Also, isn't this bloody dangerous! It seems to me it's required due to the risk of losing the incoming Neutral but I've never heard of an example of this happening in the UK?

What if you have a bloody block paving drove etc.!

To hear about it happening you would have to be listening in the right places, it's not something the media is ever going to care about or publicise.
I'm sure there are many people on this forum who have heard of it or experienced it.

If you have bloody block paving then you should clean the blood off of it, and probably be a bit more careful not to spill blood on it in the future.
 
You can drive it in with a drill but this is not best practice in-line with H&S legislation.

We hand dig with GRP fence post spades and CAT scan every 300mm.

Increasingly we are installing earth mats but these require a little more skill and expense to work with. The advantages is only need to dig to 350mm. The disadvantages is need to dig a square 1000x1000 and cost more.

I can imagine the number of earth mats installed for a domestic EV charger is probably zero!

Out of the many I've seen installed, most haven't even banged a rod in!
 
It seems to me it's required due to the risk of losing the incoming Neutral but I've never heard of an example of this happening in the UK?
The latest amendment to the wiring regs apparently (I've not done the 18th), precluded the use of a PME supply or its earthing system for car chargers (less you can achieve certain conditions). So if you have a TN-C-S it has to have a separate earth via a earth rod, unless your vehicle is being charged within the confines of the property, not on the drive for example.
Seems your electrician might be offering good advice?
 
The latest amendment to the wiring regs apparently (I've not done the 18th), precluded the use of a PME supply or its earthing system for car chargers (less you can achieve certain conditions). So if you have a TN-C-S it has to have a separate earth via a earth rod, unless your vehicle is being charged within the confines of the property, not on the drive for example.
Seems your electrician might be offering good advice?

Needless to say, I agree.

He seems like a very decent bloke.
Should I be expecting the earthing cable to be running in conduit up and into the charger.

Does it matter about the size of earthing, assuming 10mm will be ok? Or do the regs mention 16mm?

Thanks for all the information guys.
 

Reply to Earth rod installation in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
450
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
1K
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

Hi Mainline and thanks for the reply. My inverter is only fed from the mains supply over a 4 hour period at night and it does not have any tie...
Replies
8
Views
2K
Thanks all for your comments, advice and suggestions. The following is probably pretty boring for most, and is simply a summary of how the job...
Replies
8
Views
900

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top