I have just carried out an EICR.
Earthing is TT. A 4mm green/yellow conductor leaves the CU and disappears under the conservatory, I get 158Ω when I do a Ze test.
There is a 10mm that goes to both gas and water. ZS tests are around 40Ω 's on sockets/lights.
I started a similar thread some time ago
Unable to find earth rod when doing EICR - https://www.electriciansforums.net/threads/unable-to-find-earth-rod-when-doing-eicr.169576/page-6 which caused lots of discussion and most people erred towards a C3, although NV, LIM and FI were all mentioned, showing that it is a difficult one to code.
I just can't get my head around giving it a C3. It could be classed as the single most important conductor of the whole installation and I can't even get to the termination on the 'possible' earth rod to check it's ok. The termination could be appalling, I could have got 158Ω even if the 4mm conductor was just resting on the earth rod. I was going to say this is highly unlikely, but I have seen some pretty terrible terminations. Also, if the builders didn't have the knowledge to leave it accessible then I doubt they took much care when building around it. Also, builders tend to think earthing/bonding cables are not important and often just chop them off, so again, they could have done anything to it.
When I had to code serious incidents in another profession we looked at 2 influences to get a 'danger' rating.
Likelihood of occurrence and severity if it does occur.
In this case the likelihood is low (i.e termination becomes poor, may not even be an earth rod there, etc etc) but the severity is high (i.e RCD does not operate and therefore possible death under fault conditions)
I think this has to be a C2.
Putting it as an operational LIM is just ignoring the problem. NV is again ignoring the problem. FI..... possibly, but I've already investigated and the rod cannot be found.
I just need to put a new rod in, but with a C3 this may well not happen.
Would you guys still think C3??