Hello All,
I hope somebody can give me some guidance.
I have an installation that is a TT system, the area is very sandy, down the hill from the distribution board is a lake, approx 70 Meters away. The rise is about 10 metres from the lake to the level of the DB.
Next to the DB enclosure I have installed an earth rod 5/8 extendable, this is 3M deep in the ground, reading 612 ohm.
I have installed 9 x 1.2M (11M approx) 5/8 rods straight down approx 5M from DB enclosure, reading 658 ohm.
I have installed 3 lots of 3 x 1.2M (3.6M) 5/8 rods stright down at a distance of 3M apart in a triangle arrangement down at the lake level, reading 512 ohm.
I can't seem to get the reading down low enough.
Any ideas before I install enough rods to raise the copper and steel content of the area.
I hope somebody can give me some guidance.
I have an installation that is a TT system, the area is very sandy, down the hill from the distribution board is a lake, approx 70 Meters away. The rise is about 10 metres from the lake to the level of the DB.
Next to the DB enclosure I have installed an earth rod 5/8 extendable, this is 3M deep in the ground, reading 612 ohm.
I have installed 9 x 1.2M (11M approx) 5/8 rods straight down approx 5M from DB enclosure, reading 658 ohm.
I have installed 3 lots of 3 x 1.2M (3.6M) 5/8 rods stright down at a distance of 3M apart in a triangle arrangement down at the lake level, reading 512 ohm.
I can't seem to get the reading down low enough.
Any ideas before I install enough rods to raise the copper and steel content of the area.