Hello All,

I hope somebody can give me some guidance.
I have an installation that is a TT system, the area is very sandy, down the hill from the distribution board is a lake, approx 70 Meters away. The rise is about 10 metres from the lake to the level of the DB.
Next to the DB enclosure I have installed an earth rod 5/8 extendable, this is 3M deep in the ground, reading 612 ohm.
I have installed 9 x 1.2M (11M approx) 5/8 rods straight down approx 5M from DB enclosure, reading 658 ohm.
I have installed 3 lots of 3 x 1.2M (3.6M) 5/8 rods stright down at a distance of 3M apart in a triangle arrangement down at the lake level, reading 512 ohm.
I can't seem to get the reading down low enough.

Any ideas before I install enough rods to raise the copper and steel content of the area.
 
Scottish Power have put a transformer in to supply the site, they have installed a HV and a LV earth in the ground 300M away from my DB, I don't know how they arranged there earth rods, mats or whatever they used, but I was told they had a good earth.

They did have a big hole dug though.

So it can't be impossible, can it?
 
Next to the DB enclosure I have installed an earth rod 5/8 extendable, this is 3M deep in the ground, reading 612 ohm.
If you got 612 ohms with a 3 meter rod then I would whack another 3 or 4 x 2.3 meter rods on top of it and retest. I regularly need to go down at least 12-15 meters in our area which is also sand to get a decent earth reading.
 
Another variable is your test meter accuracy
[ElectriciansForums.net] Earth Rod Resistance is high
 

Reply to Earth Rod Resistance is high in the Australia area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
702
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
1K
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
3K

Similar threads

  • Question
much more information required. Is the supply to the first building a DNO supply or a sub main cable from another building ? if it is a sub main...
Replies
5
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top