Hello All,

I hope somebody can give me some guidance.
I have an installation that is a TT system, the area is very sandy, down the hill from the distribution board is a lake, approx 70 Meters away. The rise is about 10 metres from the lake to the level of the DB.
Next to the DB enclosure I have installed an earth rod 5/8 extendable, this is 3M deep in the ground, reading 612 ohm.
I have installed 9 x 1.2M (11M approx) 5/8 rods straight down approx 5M from DB enclosure, reading 658 ohm.
I have installed 3 lots of 3 x 1.2M (3.6M) 5/8 rods stright down at a distance of 3M apart in a triangle arrangement down at the lake level, reading 512 ohm.
I can't seem to get the reading down low enough.

Any ideas before I install enough rods to raise the copper and steel content of the area.
 
Sounds as if you driving into the worst type of sand, ....Washed sand that have little to no salt sulphates chlorides or minerals.... not that you would want too much sulphates and chlorides...lol!!

If after checking that your test equipment is confirmed good, then other than keep banging in rods, your only other courses are, ....Straight Chemical enhancement, Bore drilling, followed by chemically enhanced Bentonite mortar, Bore drilling followed by enhanced Conductive Portland mortar (very high carbon dust/particle content)...


Personally, i don't think i've ever had readings on any of my projects, that are as high as your reading. What may be happening is, (if there are other close by underground cables) your getting erroneous reading due to electrical noise etc... Any chance of you borrowing an earth tester, or at the very least another MFT to check your own tester against....
 

Reply to Earth Rod Resistance is high in the Australia area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
706
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
1K
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
3K

Similar threads

  • Question
much more information required. Is the supply to the first building a DNO supply or a sub main cable from another building ? if it is a sub main...
Replies
5
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top