Octopus

So I need to move / change an earth rod ......... there are a team of builders on site so anyone got any helpful pro's and con's for these things?

Ta

PS: SSE have told me I can't have PME ...
 
think a plate would be a better option than a rod or 3. all depends on the state of the ground and the depth you can get down to. could even bury some rebar as a mat with a lug welded on.
 
If building is already ongoing a earth mat on a bed of marcanite is the way to go usually gets you between 5 ohm and 30 ohm we do a lot of these as we do the temps on sites for the likes of bam Kier and laings and pme is not permitted earth spike test kit for meggers are worth weight in gold has installation got up front rcd?
 
What stage is the job at? If you can get in there when the foundation trenches are open then you can get a few rods in with a bare conductor linking them at a sensible depth along with connection(s) to the reinforcing mesh depending on the size of the installation and cost/benefit analysis.
 
Regarding earth Matt's can i use the rebar in concrete floor before concrete laid. Do you need to don't all mesh together or just clamp on to one sheet. Obliviouslt cable will be in a duct but will concrete reacted got at joint onto mesh. Seems a lot better way doing it now that knocking rods in after floor is laid
 
Get in as soon as possible, use everything that's available. Get an earth mat and a few rods in under the foundations, lug the steel formwork in any concrete work that's getting laid and connect all points using bare copper wire. Never used an earth plate TBH, assume it's just a copper sheet? Sounds expensive...
 

Reply to Earth rod(s) or earth plate(s) in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
380
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
956
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

  • Solved
There is an article about that here: https://www.cement.org/learn/concrete-technology/durability/corrosion-of-embedded-materials It states...
2
Replies
27
Views
2K
  • Question
Better/Smart/intelligent/expensive generators require two earth spikes set ~10-15m apart. They check the resistance between spikes and will...
Replies
5
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top