M

Matt Thornton

I tested a TT system today earth rod impedance was 1467 ohms, I say thats a pass ie, less than 1667 ohms, the QS at work says that it's a fail, it must be less than 200ohms......who's right ??? and why ??:confused:
 
Regulation 413-02-20 states that, for TT systems, the
value of the earth electrode resistance, R​
A (Ω),
multiplied by the operating current of the protective
device, I
n (A), must not exceed 50 V. Therefore, in the
event of a fault to earth, the RCD must operate to
prevent a danger of shock from exposed metalwork.
The resistance of the earth electrode should be less
than 50/I
n Ω; with an RCD rated at 30 mA, this
equates to approximately 1666
Ω.
Using this example, theoretically, it can be shown
that a suitably rated RCD will permit high values of
R
A, and therefore of Zs, than could be expected by
using the overcurrent devices for indirect contact
shock protection. Guidance Note 3 advises that in
practice, however, measured loop impedance values

above 200
Ω will require further investigation.
 
Sorry, forgot to say that main switch is a 100mA time delayed RCD
 
I tested a TT system today earth rod impedance was 1467 ohms, I say thats a pass ie, less than 1667 ohms


Honestly amazed at that statement:eek::eek:.

To the current edition of BS 7671 the MAX Ra (earth electrode) value is 200 ohms.

Some scheme providers say even less i.e NICEIC - 100 ohms.

With your 100mA RCD the MAX Ra you are permitted to for it to operate before fault current exceeds the safe touch voltage of 50V is 500 ohms 1667 ohms only applies when a 30mA RCD is present, which is still over the 200 ohms specified in ol'red.

So your QS is bang on...and you have a problem.
 
Honestly amazed at that statement:eek::eek:.

To the current edition of BS 7671 the MAX Ra (earth electrode) value is 200 ohms.

Some scheme providers say even less i.e NICEIC - 100 ohms.

With your 100mA RCD the MAX Ra you are permitted to for it to operate before fault current exceeds the safe touch voltage of 50V is 500 ohms 1667 ohms only applies when a 30mA RCD is present, which is still over the 200 ohms specified in ol'red.

So your QS is bang on...and you have a problem.

Pretty certain there is a table for this in the Regs and the OSG as well. Maybe someone can inform the OP what page or Regulation this falls under. (I would do but that would involve walking to the van and I'm a lazy git!)

But as mentioned the Maximum permitted is 200Ohms plus the resistance of the Rod (21 Ohms??), The 100ma RCD does equate to 500Ohms as well. So your value fails.

I suggest trying a different location for the Rod and maybe a copy of the OSG to keep hold of for the future as well.
 
Pretty certain there is a table for this in the Regs

The op should look at page 50 of the big red book table 41.5
 
Dont think the 'quick fix' solution will work on this one...even after 8 pints of stella..:D:D
 
Status
Not open for further replies.

Reply to Earth rod value ?? in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
265
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
756
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
743

Similar threads

Indeed it would be. But that would mean having 2 things to disconnect instead of one. More margin for error. Of course, any diligent spark would...
Replies
6
Views
658
loz2754
L
I opened up the CU again and the round junction box above and what I found was the blue and brown wires coming in from the wall just above the 15a...
2 3
Replies
33
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top